Discuss Block of 200+ flats, eleven single channel hot water timers blown this week alone. in the UK Electrical Forum area at ElectriciansForums.net

My thinking of what we have so far.

The catastrophic failure or the MOV (thanks) in the controller would point to a large over voltage situation.

It is most probably not environmental but a lost Neutral.

Without further information this could be anywhere internal or external.

So I was thinking to approach it on two fronts, to contact the DNO and report a possible Neutral fault whilst surveying the site, reported faults and drawings to see if a pattern can pinpoint the location.

So in a normal fault free situation the installation should look like.
20210821_084103.jpg


If the fault is in the below position then I should only be hearing of power outages in flats 7, 8 & 9 but not over voltages or the MOV failures I'm seeing.
20210821_084130.jpg


If the fault is in the below position then flats 4, 5 & 6 and flats 7, 8 & 9 will see voltage fluctuations between 0V and 400V depending on their respective loads, this situation could cause the MOV failures.
20210821_084146.jpg


And finally, in the below image the fault would be evident across all phases and all flats with under and over voltages. Whilst there are sections of the internal installation that could contain the fault; in this scenario the fault could also be external.
20210821_084200.jpg


Ii actuality I have already informed the client of the liklihood of a serious fault existing and that it may be internal or external and they will be picking it up from here.

I'm quite disappointed really as its quite interesting to see how far you can fault find on paper if you have enough information.
 

Attachments

  • 20210821_084130.jpg
    208.2 KB · Views: 4
Your explanation of the possible scenarios is correct but the configuration in pic.3 is unlikely to exist in practice. Each single phase service will be derived from a 3-phase busbar, with neutrals normally serving one or three phases but seldom two.

If the fault was a cable strike, the neutral may have not merely been broken but also shorted or arced over to a line. A variety of different voltages may have been impressed on the loads in quick succession as the fault developed.
 
I don’t think the burned out disc is an MOV. The timer uses a transformer less way of producing low voltage dc to operate the electronics. I reckon one can see a bridge rectifier - the white block component, and a disc capacitor in series with a resistor of suitable power rating together forming a mains to low voltage dropper. The placement of the resistor and the disc capacitor makes me think their right hand ends are connected to Lin and Nin respectively and their left hand ends to the ac inputs of the bridge rectifier which are normally the inner two leads for this style of rectifier. There is a smoothing capacitor to the left of the bridge rectifier. I reckon the gold rimmed cylindrical component above the relay is a battery for keep alive in the event of power cut and accumulator to handle short duration current surges when the relay turns on.
 
Last edited:
I don’t think the burned out disc is an MOV. The timer uses a transformer less way of producing low voltage dc to operate the electronics. I reckon one can see a bridge rectifier - the white block component, and a disc capacitor in series with a resistor of suitable power rating together forming a mains to low voltage dropper. The placement of the resistor and the disc capacitor makes me think their right hand ends are connected to Lin and Nin respectively and their left hand ends to the ac inputs of the bridge rectifier which are normally the inner two leads for this style of rectifier. There is a smoothing capacitor to the left of the bridge rectifier. I reckon the gold rimmed cylindrical component above the relay is a battery for keep alive in the event of power cut and accumulator to handle short duration current surges when the relay turns on.
A picture of the underside of the PCB would be handy.
 
The white block will be the dropper capacitor, the bridge rec will be SMD. But yes, let's see some pics of the PCB
 

Reply to Block of 200+ flats, eleven single channel hot water timers blown this week alone. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, I am currently in the process of estimating the electrical demand for a new construction development that will consist of an...
Replies
0
Views
847
Need help with a quote here. I’m wanting some sound advice. Was called out to the hot water not working so repaired the issue within the panel...
Replies
10
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
917
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
484
Hi everyone, I need some help with an electrical issue I'm experiencing. I recently created a new circuit for an electric oven at my friend's...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock