Currently reading:
Bodge job by NIC registered company , Help please

Discuss Bodge job by NIC registered company , Help please in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi I really could use some advive

There is a bin store near my building and the work has been done by an NICEIC company but i have made complaints to the coucil and got no where , compained twice to the company that did this work in the past 2 months and nothing has been done, i have also tried to phone the NICEIC but they say only the person who is ordering / the cient can complain.

I have listed the problems with it bellow and added some images

Conduit not continuous
Conduit not earthed
Conduit not secure
Conduit is rusting

In this state it should have been given additional protection by a 30ma RCD , in its current state there is a potential risk of electric shock if the conduit is pulled.

Whats my next move , i feel like iam banging my head against a brick wall.

Bins.jpg
IMG_0097.jpg
Conduit.jpg
IMG_0098.jpg
 
Last edited:
Hi,

The issue of it being not continuous, if I had done it it would be continuous, but maybe they had their reasons...

The fact its not secure and rusting, thats just poor workman ship, as for the rust, maybe it was a badly galvanized section..

If not RCD protected, then you would think it would need bonding really wouldnt you.
 
Yea thats my point , there is no RCD whats so ever , they have done the same kind of thing to 3 other bin stores down my road as well, it feels like this whole part-p is a joke , if i done some thing like this i would not be able to sleep at night.
 
Regardless if the conduit continuity it wouldn't require rcd protection of its surface mounted, assuming it's not for sockets, and in theory it doesn't have to be continuous, the T&E has it's own mechanical protection , although it looks rough
 
Regulation 411.4.2
Each exposed conductive part of the installation shall be connected by a protective conductor to the main earthing of the installation, which shall be connected to the earthed point of the power supply system.

Regulation 522.6.6 (iii)

The cable must be enclosed in earthed trunking or ducting
as specified in 522.6.6.(iii)

If the above where done then yes it would not require an RCD
 
It doesn't need an RCD as it is now, it just needs fixing!

An RCD does not negate the need for steel conduit to be earthed or for it to be properly constructed.

An RCD is not a magical device that excuses all bad workmanship!
 
Ok I can't even find 522.6.6 in my regs book, the nearest thing is 522.6.100 onwards which variously contain those words. But they all specifically relate to concealed cables, not surface conduit work.
 
Wel maybe you would like to read this: http://www.google.co.uk/url?sa=t&rc...zbQHBXjklYkANBA&bvm=bv.76477589,d.ZGU&cad=rja
All my point is is that the conduit has to be earthed

That link is irrelevant as it is only concerned with buried cables, not surface installations.


You are probably right that it should be earthed, but an RCD is not an alternative so fitting one will achieve nothing, so again why do you think it should have an RCD fitted?

I say probably as it is obviously T&E inside the conduit, which is a wiring system in its own right, so it is possible that there could be some debate from some quarters as to whether it needs earthing or bonding or neither.

Also as T&E is suitable for use without additional mechanical protection there is no requirement for the conduit to pass through the doorframe.
 
Yes but as the conduit is insecure and the cable could be pulled out if the light fitting , and the line condutor could be toching the unearthed conduit .Am i the only one who can see some one getting an electric shock?

And yes i agree if the conduit was secure and continious then there is no need for an RCD , but the conduit has never been earthed or mechanicly or electricy continious.
 

Reply to Bodge job by NIC registered company , Help please in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top