Discuss Bodge job by NIC registered company , Help please in the UK Electrical Forum area at ElectriciansForums.net

Regulation 411.4.2
Each exposed conductive part of the installation shall be connected by a protective conductor to the main earthing of the installation, which shall be connected to the earthed point of the power supply system.

Regulation 522.6.6 (iii)

The cable must be enclosed in earthed trunking or ducting
as specified in 522.6.6.(iii)

If the above where done then yes it would not require an RCD
 
It doesn't need an RCD as it is now, it just needs fixing!

An RCD does not negate the need for steel conduit to be earthed or for it to be properly constructed.

An RCD is not a magical device that excuses all bad workmanship!
 
Ok I can't even find 522.6.6 in my regs book, the nearest thing is 522.6.100 onwards which variously contain those words. But they all specifically relate to concealed cables, not surface conduit work.
 
Wel maybe you would like to read this: http://www.google.co.uk/url?sa=t&rc...zbQHBXjklYkANBA&bvm=bv.76477589,d.ZGU&cad=rja
All my point is is that the conduit has to be earthed
 
What's occurring in the 2nd picture where the tube is cut off?
Where are the cables going?

522.6.6.200 says it should be coloured in brick pattern paint. Fail!
 
Wel maybe you would like to read this: http://www.google.co.uk/url?sa=t&rc...zbQHBXjklYkANBA&bvm=bv.76477589,d.ZGU&cad=rja
All my point is is that the conduit has to be earthed

That link is irrelevant as it is only concerned with buried cables, not surface installations.


You are probably right that it should be earthed, but an RCD is not an alternative so fitting one will achieve nothing, so again why do you think it should have an RCD fitted?

I say probably as it is obviously T&E inside the conduit, which is a wiring system in its own right, so it is possible that there could be some debate from some quarters as to whether it needs earthing or bonding or neither.

Also as T&E is suitable for use without additional mechanical protection there is no requirement for the conduit to pass through the doorframe.
 
Yes but as the conduit is insecure and the cable could be pulled out if the light fitting , and the line condutor could be toching the unearthed conduit .Am i the only one who can see some one getting an electric shock?

And yes i agree if the conduit was secure and continious then there is no need for an RCD , but the conduit has never been earthed or mechanicly or electricy continious.
 

Reply to Bodge job by NIC registered company , Help please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
843
I have been working as an electrician under an NICEIC Approved Contractor for the past 10 years. I have my C&G2365 level 1/2/3 (acquired before...
Replies
1
Views
1K
Hi, I am just wondering if there is anybody out there interested in allowing me to do a little voluntary work with your company to gain a little...
Replies
0
Views
196
Hi Everyone, Last year arranged for my mother's and my consumer units to be changed by the same electrician who is NICEIC registered. Both jobs...
Replies
20
Views
2K
Hi guys, I don’t really know where to post this, sorry if it’s in the wrong place. After posting a thread about old lead sheathed cable in my...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock