Hi sorry very long one. Please hop to bottom paragraph for short version. I’m just about to refurb bathroom in my 1986 house but bonding always confused me and I am still confused now! So my main incoming water pipe (extraneous) is Currently bonded To MET in 10mm and hot and cold pipes cross bonded near to main bond clamp. My gas pipe is also bonded to MET with 10mm. A stainless steel sink in small utility room is bonded ( I did that over 20 years ago) with the copper pipes as it has with plastic between pipes and sink. The bathroom has a shaver socket and Water based radiator with copper pipes, I see no signs of supplementary bonding.

i think bonding sinks is a very old requirement and I also believe water main with plastic incoming pipe no longer requires bonding.

But if the sink and main water is not bonded and there are plastic pipes section in and around the plumbing system what would happen if a fault condition eg cable touching copper pipe or sink occurred? The house is 1986 and all circuits protected by a single RCD 30ma but if the sink and some of the main Copper pipework is not earthed I guess the rcd wouldn’t detect leakage and would sit at mains voltage? Is that right? Only when someone came along and touched the pipe or sink would rcd hopefully trip (they can go wrong themselves).

I guess what I am asking is there a good reason NOT to have Steel sink and main water incomer bonded to MET? I know it’s not stipulated by regs but in this case I can see a benefit of doing it. Also given the lack of electrical equipment in bathroom and the fact the rcd protects all circuits, is the lack of supplementary bonding there OK?
 
Yea old school sparkies would bond the water but the requirement now like you said, if it’s a plastic entry into building it now does not require bonding.
Mixture of metal & plastic piping is irrelevant.
The answer I got of the Niceic is that any metalwork regarding those pipes will for fortuitously earthed elsewhere by boiler, Imm heater, washing machine etc.
It’s not a extraneous part & no bonding required.
 
Mixture of metal & plastic piping is irrelevant.
The answer I got of the Niceic is that any metalwork regarding those pipes will for fortuitously earthed elsewhere by boiler, Imm heater, washing machine etc.
Given a washing machine is connected to the water pipe with a rubber hose how do the NICEIC think the washing machine fortuitously earth's the copper pipework
 
thx all. i understand there is no longer a requirement to bond kitchen sink or water pipe if plastic entering building. but if this metal is not now extraneous (outside building) AND not exposed conductive part of part of electrical installation iit can sit there unbonded and become live in fault condition? Does this mean no overcurrent device (mcb) would operate neither earth leakage ( rcd). ONLY when somone grounded that faulty live metalwork would the fuse/ mcb or rcd operate? we laughed back in day when 15th edition said to bond everything but this does seem rather odd! I will leave the sink bond in then BUT is there a reason (safety) why I shouldnt? i appreciate its not in regs.
 
thx all. i understand there is no longer a requirement to bond kitchen sink or water pipe if plastic entering building. but if this metal is not now extraneous (outside building) AND not exposed conductive part of part of electrical installation iit can sit there unbonded and become live in fault condition? Does this mean no overcurrent device (mcb) would operate neither earth leakage ( rcd). ONLY when somone grounded that faulty live metalwork would the fuse/ mcb or rcd operate? we laughed back in day when 15th edition said to bond everything but this does seem rather odd! I will leave the sink bond in then BUT is there a reason (safety) why I shouldnt? i appreciate its not in regs.

Part of the problem is that by bonding bits of random metalwork, you are connecting them to the electrical system. Now admittedly this should never be a problem, but dont forget that the installation earth is not always at 0v when there is a fault condition, and the voltage on these metal parts will rise.
 
Good point. Damned if we do damned if we do the then! I guess my question is which is the more likely fault condition..an earth fault on main installation which raises its potential and that of any bonded metalwork OR a fault within the installation (e.g. pipe touched by cable) which raises significantly the potential of the various non-bonded metalwork In the building.

Guess it’s all academic on my installation as everything is protected by 30ma rcd anyway (assuming rcd doesn’t fail at same time as fault condition occurs which is less likely than me winning euro millions tomorrow)
 
Good point. Damned if we do damned if we do the then! I guess my question is which is the more likely fault condition..an earth fault on main installation which raises its potential and that of any bonded metalwork OR a fault within the installation (e.g. pipe touched by cable) which raises significantly the potential of the various non-bonded metalwork In the building.

Guess it’s all academic on my installation as everything is protected by 30ma rcd anyway (assuming rcd doesn’t fail at same time as fault condition occurs which is less likely than me winning euro millions tomorrow)

I'd mention that faulty RCDs are not uncommon, but I wouldn't want to worry you ?

I gurss the important thing is to keep your electrical system safe and have it checked periodically. Also dont forget to test RCDs with the button every now and again.
 
? I used to it all my own electrical work given I was a time served sparky once upon a time (mainly industrial though). I need to change cu now to increase number of RCD, I only have one at the moment, maybe add RCBOs and add a new circuit to shed. I was thinking of buying MFT but at £500 for a cheaper one and the fact that even after doing the job properly and testing it, it still doesn’t comply with building regs because I’m not certified means I’ve got to pay someone. Council want £477just to test! Thing is that these regs are here to improve safety but in reality how many people will just bung it in to save money. It does rankle a bit to think that I did 4-5 years of training/ studying and can’t legally change a cu myself without paying a lot to someone to test it! I wonder if I accidentally smashed the plastic cu enclosure with a hammer if I could legally change it as an emergency procedure??
 
Hi sorry very long one. Please hop to bottom paragraph for short version. I’m just about to refurb bathroom in my 1986 house but bonding always confused me and I am still confused now! So my main incoming water pipe (extraneous) is Currently bonded To MET in 10mm and hot and cold pipes cross bonded near to main bond clamp. My gas pipe is also bonded to MET with 10mm. A stainless steel sink in small utility room is bonded ( I did that over 20 years ago) with the copper pipes as it has with plastic between pipes and sink. The bathroom has a shaver socket and Water based radiator with copper pipes, I see no signs of supplementary bonding.

i think bonding sinks is a very old requirement and I also believe water main with plastic incoming pipe no longer requires bonding.

But if the sink and main water is not bonded and there are plastic pipes section in and around the plumbing system what would happen if a fault condition eg cable touching copper pipe or sink occurred? The house is 1986 and all circuits protected by a single RCD 30ma but if the sink and some of the main Copper pipework is not earthed I guess the rcd wouldn’t detect leakage and would sit at mains voltage? Is that right? Only when someone came along and touched the pipe or sink would rcd hopefully trip (they can go wrong themselves).

I guess what I am asking is there a good reason NOT to have Steel sink and main water incomer bonded to MET? I know it’s not stipulated by regs but in this case I can see a benefit of doing it. Also given the lack of electrical equipment in bathroom and the fact the rcd protects all circuits, is the lack of supplementary bonding there OK?
Have you tested the sink to see if it requires bonding?
'
 
I thought the regulation states kitchen sinks don’t require bonding? would a test be useful because things may well change in future especially with introduction of plastic pipe into copper pipe systems.

They don't specifically need bonding. But any extraneous metal parts may need bonding. The sink is unlikely to be an extraneous conductive part.
 
I've always understood extraneous to be introduced from the outside ie not connected to the electrical installation. If a lead or metal pipe were used as drainage, then it may be extraneous.

That's what I was getting at, but I maybe didn't put it too well.
 
They don't specifically need bonding. But any extraneous metal parts may need bonding. The sink is unlikely to be an extraneous conductive part.
this is where i get really confused. im going to get somwone to do the job anyway but for my own sanity is there an explicit definition of "extraneous metal part"? i thought it was a conductive "thing" that enters the location (house) which may introduce a separate connection to earth and therefore may have different potential to MET. in my case this is ONLY the gas pipe (assuming its metal) but NOT my water main as that is plastic at point of ingres to the house. BUT then the gas pipe connects to boiler along with all CH pipes so are those, up to any point at which they become isolated by plastic pipe are also extraneous?Is then the hot water pipe from copper cylinder are also extraneous along with any water pipe that has a conductive path eg.copper hot water pipe to brass tap mixer which in turn has copper connection to cold water pipe.... and so on? my head hurts
 
Albeit about protective supplementary bonding and RCD, Chris's vid explains extraneous conductive parts.

Thanks for that it is one I had seen . It says at 2.00 that any less than 1667ohms no bonding required (assuming rcd 30ma). At the end it says less than .02MOhms you do need to bond and above you don’t? Both say measure Between Known earth in the room and lump of metal you want to know whether to bond or not.
 
this is where i get really confused. im going to get somwone to do the job anyway but for my own sanity is there an explicit definition of "extraneous metal part"? i thought it was a conductive "thing" that enters the location (house) which may introduce a separate connection to earth and therefore may have different potential to MET. in my case this is ONLY the gas pipe (assuming its metal) but NOT my water main as that is plastic at point of ingres to the house. BUT then the gas pipe connects to boiler along with all CH pipes so are those, up to any point at which they become isolated by plastic pipe are also extraneous?Is then the hot water pipe from copper cylinder are also extraneous along with any water pipe that has a conductive path eg.copper hot water pipe to brass tap mixer which in turn has copper connection to cold water pipe.... and so on? my head hurts

There is no need to be confused, it really is very simple and you are rather over thinking it. An extraneous conductive part is defined as a metallic part which is not part of the electrical installation but which may introduce a potential, usually earth.
Consider a 'normal' building. Floors walls and ceilings are generally constructed of materials with a high resistance and low conductivity. An external metallic service entering the building is likely to introduce an earth potential by virtue of being in contact with the ground, so it is main bonded to the MET at the point of entry, beyond this point any metallic pipework is likely to be within the confines of an electrically insulated building and so should not pick up an external potential. The hazard has been dealt with at the point of entry, it matters not what any pipework does within the building from an electrical point of view. The common misconception that bonding is to prevent pipework becoming 'live' is totally incorrect. Other requirements are in place to prevent that, such as wiring being kept apart from other services. Where a conductive part such as an immersion heater, or motorised valve is connected to metallic pipework the pipe will be earthed because it is physically connected to the conductive part, and so will be protected against a fault to earth, but that is not the same as bonding.
Supplementary bonding is an additional measure only likely to be required in special locations, which do not include kitchens. I cannot think of a single instance where bonding a kitchen sink would be required. Even if the sink was tested and found to be extraneous it is almost certain that whatever the sink was attached to (pipe...structural steel etc) would be extraneous...NOT the sink. And of course an incoming metallic pipe or structural steel will have been or should have been main bonded anyway.
Far too much is made of testing to see if something is extraneous. It is nearly ALWAYS possible to ascertain whether bonding is required simply be observation of building structure and incoming services. Testing is nearly always misleading because of parallel paths. For example consider testing a heating pipe. It is likely to to be physically but indirectly connected to a gas service which whether bonded or not will be 'earthy'. The gas service will clearly need bonding, but a test may show the heating pipe should also be bonded. Simple observation will show the gas pipe is coming in from externally, in contact with the ground and will require bonding, but the heating pipes are completely within the confines of the building and cannot introduce an external potential.
 
I think he does. I think he was doing the same as me - pointing the OP towards what might be extraneous and what can't be.
Doesn't seem much point in pointing the OP to test something which will not require bonding but which the suggested test may indicate to the OP that it should be bonded. Just going to confuse him more.
 
Doesn't seem much point in pointing the OP to test something which will not require bonding but which the suggested test may indicate to the OP that it should be bonded. Just going to confuse him more.

Not so much test it, but to consider why theres no point bonding it.
 
thx all. i understand there is no longer a requirement to bond kitchen sink or water pipe if plastic entering building. but if this metal is not now extraneous (outside building) AND not exposed conductive part of part of electrical installation iit can sit there unbonded and become live in fault condition? Does this mean no overcurrent device (mcb) would operate neither earth leakage ( rcd). ONLY when somone grounded that faulty live metalwork would the fuse/ mcb or rcd operate? we laughed back in day when 15th edition said to bond everything but this does seem rather odd! I will leave the sink bond in then BUT is there a reason (safety) why I shouldnt? i appreciate its not in regs.
"To Bond or not to Bond ,that is the question".

I wonder if there is another forum in the world outside the UK and ROI that gives this topic the level of attention we do.I may be corrected by my UK colleagues here ,but I dont believe there is.I have worked in a number of countries in Europe and beyond and the amount of " green/yellow" cable bonds I have seen is a small fraction of what we are used to seeing here.

Your point about the 15th th edition being regarded as OTT in relation to bonding is well made.Over here in the ROI we have just being informed that as of february 2021 we are no longer required to bond sinks ( no that is not a misprint.It really is 2021 ,not 2001). Despite the fact that they have being plumbed in plastic since the 1990,s.
I personally have being banging on the inspectors doors for a number of years in relation to the isssue. What gets to me is the fact that we now have arbitrary regs about either bonding or not bonding sinks , when in reality its the electrical principle of " is it extraneous or not " that should always be the determining factor.
 
Reading about this for a while now. Still none the wiser about whether bonding is required in bathroom or when. At least I know kitchens and water mains with plastic at point of Ingres don’t need it (I’m going to leave it in for now though.

Read on one forum that there was a Poor unfortunate girl sat on sink (earthed) put hand in toaster current flowed and girl died. Wow. Very sad.not sure whether it’s true.

Conversely, if a strange fault occurred making unearthed sink live someone could get shock from it. I have rcd protection on all circuits so guess I need not worry too much.

Either case is very unlikely but in case of the poor girl this was the reality. I suppose all this earthing stuff is about mitigating risks however unlikely it be.
 
There is no need to be confused, it really is very simple and you are rather over thinking it. An extraneous conductive part is defined as a metallic part which is not part of the electrical installation but which may introduce a potential, usually earth.
Consider a 'normal' building. Floors walls and ceilings are generally constructed of materials with a high resistance and low conductivity. An external metallic service entering the building is likely to introduce an earth potential by virtue of being in contact with the ground, so it is main bonded to the MET at the point of entry, beyond this point any metallic pipework is likely to be within the confines of an electrically insulated building and so should not pick up an external potential. The hazard has been dealt with at the point of entry, it matters not what any pipework does within the building from an electrical point of view. The common misconception that bonding is to prevent pipework becoming 'live' is totally incorrect. Other requirements are in place to prevent that, such as wiring being kept apart from other services. Where a conductive part such as an immersion heater, or motorised valve is connected to metallic pipework the pipe will be earthed because it is physically connected to the conductive part, and so will be protected against a fault to earth, but that is not the same as bonding.
Supplementary bonding is an additional measure only likely to be required in special locations, which do not include kitchens. I cannot think of a single instance where bonding a kitchen sink would be required. Even if the sink was tested and found to be extraneous it is almost certain that whatever the sink was attached to (pipe...structural steel etc) would be extraneous...NOT the sink. And of course an incoming metallic pipe or structural steel will have been or should have been main bonded anyway.
Far too much is made of testing to see if something is extraneous. It is nearly ALWAYS possible to ascertain whether bonding is required simply be observation of building structure and incoming services. Testing is nearly always misleading because of parallel paths. For example consider testing a heating pipe. It is likely to to be physically but indirectly connected to a gas service which whether bonded or not will be 'earthy'. The gas service will clearly need bonding, but a test may show the heating pipe should also be bonded. Simple observation will show the gas pipe is coming in from externally, in contact with the ground and will require bonding, but the heating pipes are completely within the confines of the building and cannot introduce an external potential.
Thanks?. I’m only trying to understand it so probs am overthinking it. However, if you take a look around at the many forums where the topic has been discussed you will see that it may not be as clear to many people as it is to you
 
However, if you take a look around at the many forums where the topic has been discussed you will see that it may not be as clear to many people as it is to you
I am a relative newcomer to this forum myself and its standard of teaching is in my humble opinion second to none. Ever being involved in discussions where you feel you are just "going around in circles"?. Or you ask a question only to end up with 2 more questions rather than an answer?
You have arrived on a site where the "ifs, buts and maybys" are gradually taken out of the equation through sound logical reasoning. You already experienced that from the replies on this thread. Take a look at the older posts on the same topic. Believe me, in a matter of weeks your uncertainties about bonding will be history
 
I certainly hope so. Although I only started looking at this as I’m just about to refurb bathroom and also want to change CU. Once I’ve done those I guess my involvement in electrical work will cease. As it turns out I cannot legally do the latter in a cost effective manner, so will either have to abandon that and keep my plastic enclosure, single rcd for all circuits system, or get someone in to do it. The supplementary bonding in bathroom still confuses me as on another forum with quotes from regs, it appears supp bonding cannot be omitted without main equipotential bonding :) I’ll have a rest and take another look at that later.

Thanks for clarifying “extraneous” as that was confusing me. Btw Is extraneous in a special location the same or is it extraneous to the location, in my case bathroom?
 
Thanks for that it is one I had seen . It says at 2.00 that any less than 1667ohms no bonding required (assuming rcd 30ma). At the end it says less than .02MOhms you do need to bond and above you don’t? Both say measure Between Known earth in the room and lump of metal you want to know whether to bond or not.
He said that between below 0.02mohms and above 1667ohms, would need bonding. However, bear in mind the accuracy of using IR tester of measuring ohms.

I don’t agree with not testing to discover if something is extraneous or not though. It depends on the property. In my three year old house, all pipework is plastic, except the internal gas, and short pieces of copper to shower valves. So no reason to test. But in older houses, with all copper pipes, with routes unknown unknown, such a test is the only way to confirm IMO.
 
Thanks for clarifying “extraneous” as that was confusing me. Btw Is extraneous in a special location the same or is it extraneous to the location, in my case bathroom?
"extraneous" technically is defined as metalwork that could "introduce a potential" usually earth potential. I have also noticed that some forums have applied it in its dictionary sense of "originating from outside". However electrically speaking metalwork "originating from outside" but that "cannot introduce a potential" is not what is electricians consider as extraneous. You can simplfy the matter for yourself by simply carrying out an IR test on the metalwork in question. Isolated metalwork will likely give either an "infinity" or an extremely high megaohm reading. Metalwork that gives a lower reading (30,000 ohms for instance) though technically "extraneous" is not required to be bonded in UK as that resistance is deemed too high to allow a dangerous shock to occur. I believe the cutoff point in UK to be around 22,000 ohms. I, m sure other posters will confirm
 
Earthing and Bonding.....here we go. It's a case of having a read and sort out the difference between them. As indicated, find some old threads on the subject.

Back to the 15th..... Earthing? Just bond it....he, he! ?

Remember taking earth wires from the nearest point to bond radiators, for example.

IMG_1126.jpg


Wrong with this sketch...you'd have to unplug the kettle to reach the tap and refill it, thus eliminating the problem.
It's a guide, by the way, not the actual regs.
 
He said that between below 0.02mohms and above 1667ohms, would need bonding. However, bear in mind the accuracy of using IR tester of measuring ohms.

I don’t agree with not testing to discover if something is extraneous or not though. It depends on the property. In my three year old house, all pipework is plastic, except the internal gas, and short pieces of copper to shower valves. So no reason to test. But in older houses, with all copper pipes, with routes unknown unknown, such a test is the only way to confirm IMO.
I would like to test for interest more than anything as I have a 1986 house with copper pipe throughout but with some plastic additions that I have made over the years. However all CH pipes are connected to bonded gas main pipe via boiler and copper hot water tank. Assuming the flexible hoses ( ones with steel braiding) are conductive then the cold water pipes are connected to hot water pipes via those through the mixer taps, apart from útil room where I used plastic flex is for some reason. So electrically the whole copper pipe system will be at same potential (met bonded to gas). That’s without the current bond on the cold water main (no longer required apparently as it is plastic incomer) and the cross bonding between hot and cold that exists under sink in útil room and also by stop cock. Therefore without disconnecting these pipes and “bonds” the test would be pointless as the reading to MET will be very low. Oh and one other point which would make testing difficult, I don’t own a IR or MFT tester? given I have to get someone in to test whatever work is done so I’m not going to fork out for one now As I have to spend that money on a more modern up to date sparks than me:) shame that I like new toys.
 

Reply to Bond sinks and mains water with plastic at start in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
938
No waffling, going to get straight to the point. Main water on the exterior of the building in plastic. Changes to copper inside the building...
Replies
24
Views
921
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Replies
6
Views
415
So I know why it is done, where it is done and how it’s done, but I’m yet to see a scenario where there is shock danger in a typical bathroom in a...
Replies
32
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock