Discuss bonding across plastic pipe joint, instead of supplementary bond in the Industrial Electricians' Talk area at ElectriciansForums.net

1Justin

-
Arms
Reaction score
157
New shaver socket outside zone in bathroom. (FCU outside the room,17th ed'n board).
Checking the bathroom to see if any supplementary bonding needed, turned out the sink and bath taps were hovering at about 5K Ohm (ie >1667 and < 22K).

Turns out the owner had interrupted the hot and cold Cu pipes with single push-fittings in the loft, and that was the source. (Main equipotential bonding was very effective before then, rest of the house all in Cu). So Supplementary bonding required in bathroom, but this would have been VERY disruptive, and customer wouldn't take it on.

Easy however to bond across the two plastic joints in the attic with 10mm strap and clamps. Nice and neat, very effective and safely out of the way. Bathroom taps are no longer Extraneous, at a small fraction of an ohm.

So technically I don't see this as any different to what I might have found had the plastic parts not been there, and (just say) a compression joint had provided a low enough resistance. I'd have measured it, then been none the wiser and equally wouldn't have fitted any Supplementary bonding.

Where do I sit with this re 701.415.2? Part Vi just says "effectively connected", which it is. - but it's not supplementary bonding.

Chasing walls/tiles off etc to get the cable in wasn't going to happen.

Might I record this as a departure, and get on with things?
 
New shaver socket outside zone in bathroom. (FCU outside the room,17th ed'n board).
Checking the bathroom to see if any supplementary bonding needed, turned out the sink and bath taps were hovering at about 5K Ohm (ie >1667 and < 22K).

Turns out the owner had interrupted the hot and cold Cu pipes with single push-fittings in the loft, and that was the source. (Main equipotential bonding was very effective before then, rest of the house all in Cu). So Supplementary bonding required in bathroom, but this would have been VERY disruptive, and customer wouldn't take it on.
It does not affect the Main Bonding either way.
Supplementary Bonding doesn't have to be IN the bathroom as long as it bonds parts which are.

Easy however to bond across the two plastic joints in the attic with 10mm strap and clamps. Nice and neat, very effective and safely out of the way. Bathroom taps are no longer Extraneous, at a small fraction of an ohm.
They are still extraneous but now effectively bonded.
You didn't need 10mm.

So technically I don't see this as any different to what I might have found had the plastic parts not been there, and (just say) a compression joint had provided a low enough resistance. I'd have measured it, then been none the wiser and equally wouldn't have fitted any Supplementary bonding.
They may be now effectively connected to the MET (if <50/Ia) but have you checked that the measurements between parts and between parts and CPCs are also less than 50/Ia?

Where do I sit with this re 701.415.2? Part Vi just says "effectively connected", which it is. - but it's not supplementary bonding.
Yes it is.

Might I record this as a departure, and get on with things?
No, it does not affect the Main Bonding requirement.
 
Just to add for clarification -

As far as Main Bonding is concerned, it does not matter what happens within the premises.

Because it is a bathroom, Supplementary Bonding may be required to ensure there is no (or the allowed maximum) potential difference between simultaneously accessible extraneous and exposed parts - 50/Ia.

You may have been able to achieve the same result by connecting the pipe to another which did not have a plastic joint but it's the same difference.
 
  • Where do I sit with this re 701.415.2? Part Vi just says "effectively connected", which it is. - but it's not supplementary bonding.
Yes it is.
Hmm, but this bonding strap doesn't connect to local CPC of "Each Circuit" (except via the MET via main bonding where it does connect then to all circuits). This is why I would hesitate to call it "Supplementary Bonding". It is nonetheless "Effective" (as might have been a plumbing compression joint in the same location).
(BTW between parts and to local CPC all now very solid and low resistance)
 
Hmm, but this bonding strap doesn't connect to local CPC of "Each Circuit"
If the results are that it is now satisfactorily (supplementery) bonded, then it does.
Other parts - pipes and CPCs can be used as the supplementary bonding conductors.
You don't have to individually connect each extraneous and exposed part and CPC to every other extraneous and exposed part and CPC (lots of stars) - just connect them together (ring).
So this pipe entering the bathroom with unsatisfactory connection to earth could have been made satisfactory by connecting it to other parts.
You achieved the result by bridging the plastic joint which is fine.

(except via the MET via main bonding where it does connect then to all circuits).
Then it does which is acceptable.

This is why I would hesitate to call it "Supplementary Bonding". It is nonetheless "Effective" (as might have been a plumbing compression joint in the same location).
But it is Supplementary Bonding because you did it to ensure satisfactory bonding in the bathroom.
If it were not a bathroom, you wouldn't even have tested it and it wouldn't matter.

The pipe is Main Bonded where it enters the premises - no more Main Bonding (10mm to the MET) is required inside the premises.

If it had been a compression joint then perhaps Supplementary Bonding would not be required at all because the pipe was the conductor.
Certainly no more Main Bonding would be required.


(BTW between parts and to local CPC all now very solid and low resistance)
Good, so mission accomplished.

Just a confusion in terms.
 

Reply to bonding across plastic pipe joint, instead of supplementary bond in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
Disclaimer: I'm not going to attempt this job myself, I want a professional to do this job properly since I consider it non-trivial and need it...
Replies
2
Views
922
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Good morning everyone. I’m looking at getting an EV charger installed at my home and the company is requesting that I earth bond my water supply...
Replies
8
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock