Discuss bonding in detached garage in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

R

Robo

TNCS supply.

Iv been asked to do an eicr.The garage is connect to house using 6mm 3c swa. There a plastic waterpipe which enters the garage. then goes to a sink and toilet which has some exposed copper sections on show. Do they need bonding? Both house and garage have rcd protection
 
IR test between the melal pipework and your earth terminal. if rfeading is > 22k ohms, not extraneous so no need to bond.
 
The question is the service extraneous......unlikely if plastic. The exposed copper sections are also unlikely to be extraneous unless they are in contact with the ground or structural steel. If the garage is steel framed that may require main bonding. It is possible to test for ECP's. IR test between suspected ECP's and the MET. Less than 22Kohms is assumed ECP and needs bonding.
One point is that you state 6.0mm SWA.....this will not be suitable as a main bond to ECP's if the supply is TNCS....a minimum 10.0mm copper will be required back to the MET at the intake.

Edit...tel types quicker lol.
 
So if i IR test between earth terminal in garage and ECP (sections of exposed copper pipe near sink) the reading needs to be above 22 kiloohms 22000 ohms and i dont need to bond. But if its below that i will need to put a 10mm earth in from the MET at the house.?

Will this method apply with regards to the copper bath to.

thanks
 
So if i IR test between earth terminal in garage and ECP (sections of exposed copper pipe near sink) the reading needs to be above 22 kiloohms 22000 ohms and i dont need to bond. But if its below that i will need to put a 10mm earth in from the MET at the house.?

Will this method apply with regards to the copper bath to.

thanks

That earth terminal in the garage is your Earth Marshaling Point (EMP) your MET is most likely at the origin of the installation in the house. You need to test there
 

Reply to bonding in detached garage in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
610
I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit...
Replies
3
Views
771
I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
730
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
447

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock