Discuss Bonding installed, which cert to use? in the UK Electrical Forum area at ElectriciansForums.net

robd

-
Arms
Reaction score
339
Afternoon all. Have recently installed bonding to water in each flat in a block of flats as part of some remedial work from an EICR. Need to give landlords some paperwork to say work is done, just wondered on your thoughts as to what to give to him. Seems a bit excessive to fill out a whole EIC just to fill out the box saying bonding size, type and continuity confirmed. Cheers
 
I would have thought it would need to be a EIC, most of the data from the EICR could be used if it was current, the only part you should be filling would relate to the new work of the bonding, so no need to fill out the info on the CU etc.,
 

Reply to Bonding installed, which cert to use? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning all. I was chatting with another spark the other day and he’s telling me I’m making excessive work for myself by issuing minor works...
Replies
11
Views
3K
Evening all, I just wanted to see if electrical improvers/adult trainees with appropriate levels of experience and who hold testing...
Replies
0
Views
1K
As above ,does any of the following work require a minor work cert, changing MCB's, changing sockets, fitting CU blanks, filling CU holes with...
Replies
5
Views
1K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
893
Evening all, Recently started working for a company carrying out electrical installations - I've found a job today that didn't have any bonding...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock