Discuss Bonding of conduit in kitchen floor in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
62
Bit of a debate today, advice please as regs book not possible to get in my hands until tomorrow. New job, apartments, in the kitchen there are 2 x 25mm conduits from an external wall to an island within the kitchen that is free standing, to be able to get the hob supply across and lighting with a spare in case any sockets are added at a later date. My question is, do these require bonding? Thanks in advance.
 
If they are in good contact with earth(generally below the foundations) and meet the definition of an extraneous conductive part then They will require protective bonding to the MET
 
Bit of a debate today, advice please as regs book not possible to get in my hands until tomorrow. New job, apartments, in the kitchen there are 2 x 25mm conduits from an external wall to an island within the kitchen that is free standing, to be able to get the hob supply across and lighting with a spare in case any sockets are added at a later date. My question is, do these require bonding? Thanks in advance.
Have you tested the conduits to see if they are extraneous?
 
New posts

Reply to Bonding of conduit in kitchen floor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
260
Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Replies
2
Views
1K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
910
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock