Bit of a debate today, advice please as regs book not possible to get in my hands until tomorrow. New job, apartments, in the kitchen there are 2 x 25mm conduits from an external wall to an island within the kitchen that is free standing, to be able to get the hob supply across and lighting with a spare in case any sockets are added at a later date. My question is, do these require bonding? Thanks in advance.
 
If they are in good contact with earth(generally below the foundations) and meet the definition of an extraneous conductive part then They will require protective bonding to the MET
 
If they are in good contact with earth(generally below the foundations) and meet the definition of an extraneous conductive part then They will require protective bonding to the MET

They cant be an extraneous conductive part by definition if they are part of the electrical system.
As Andy has said. They require earthing.
 
Bit of a debate today, advice please as regs book not possible to get in my hands until tomorrow. New job, apartments, in the kitchen there are 2 x 25mm conduits from an external wall to an island within the kitchen that is free standing, to be able to get the hob supply across and lighting with a spare in case any sockets are added at a later date. My question is, do these require bonding? Thanks in advance.
Have you tested the conduits to see if they are extraneous?
 
If the cable installed inside the conduit is insulated and sheathed such as twin&earth , then does it still need to be earthed as you effectively have double insulation unlike singles?
 
Try regulation 412.1.1 double or reinforced insulation
Basic protection and fault protection are provided by reinforced insulation between live parts and accessible parts.
Regulation 412.2.

Singles don’t have reinforced insulation so understandably need containment as per regulation 521.10.1,where as twin and earth does, so I’d say it’s not necessarily a requirement to Earth the conduit if metal containing insulated and sheathed cables
 
Last edited:
As far as I can see, the reg that requires the earthing of exposed conductive parts is all encompassing and makes no exceptions.

The debate would be whether a part is an exposed conductive one or not.
 
Well as per guidance note 8 and regulation 412.2.4.1 A cable complying with the appropriate standards having a non metallic sheath is deemed to provide satisfactory basic protection and fault protection as does an item of class 2 equipment.
Class 2 equivalence aas pvc insulated and sheathed cables.
Hence containment such as metal tray or basket need not be earthed.
Cables in conduit are fully enclosed but I feel meet the same requirement
 
411.3.1.1 is the reg that asks for earthing of exposed conductive parts. It makes no exception I can see nor references any of the regs pertaining to reinforced or double insulation.
 
Try regulation 412.1.1 double or reinforced insulation
Basic protection and fault protection are provided by reinforced insulation between live parts and accessible parts.
Regulation 412.2.

Singles don’t have reinforced insulation so understandably need containment as per regulation 521.10.1,where as twin and earth does, so I’d say it’s not necessarily a requirement to Earth the conduit if metal containing insulated and sheathed cables
T&E does not have reinforced insulation it has one layer of electrical insulation and an overall sheath which provides protection for the electrical insulation.
 

Reply to Bonding of conduit in kitchen floor in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock