Search the forum,

Discuss Bonding of conduit in kitchen floor in the UK Electrical Forum area at ElectriciansForums.net

As far as I can see, the reg that requires the earthing of exposed conductive parts is all encompassing and makes no exceptions.

The debate would be whether a part is an exposed conductive one or not.
 
That was my point but you made it in a much less smart arsey way. :)

I blame too much paperwork.

my apologies to Ian for said smart arse manner. :)
 
Well as per guidance note 8 and regulation 412.2.4.1 A cable complying with the appropriate standards having a non metallic sheath is deemed to provide satisfactory basic protection and fault protection as does an item of class 2 equipment.
Class 2 equivalence aas pvc insulated and sheathed cables.
Hence containment such as metal tray or basket need not be earthed.
Cables in conduit are fully enclosed but I feel meet the same requirement
 
411.3.1.1 is the reg that asks for earthing of exposed conductive parts. It makes no exception I can see nor references any of the regs pertaining to reinforced or double insulation.
 
Try regulation 412.1.1 double or reinforced insulation
Basic protection and fault protection are provided by reinforced insulation between live parts and accessible parts.
Regulation 412.2.

Singles don’t have reinforced insulation so understandably need containment as per regulation 521.10.1,where as twin and earth does, so I’d say it’s not necessarily a requirement to Earth the conduit if metal containing insulated and sheathed cables
T&E does not have reinforced insulation it has one layer of electrical insulation and an overall sheath which provides protection for the electrical insulation.
 
Well it’s deemed to provide satisfactory basic and fault protection as does an item of class 2 equipment.
I’m aware that every one bangs on about twin and earth is not class 2 blah blah but there it is.
Check out guidance note 8
 
On second thoughts, I don't think T&E does satisfy the requirement to deemed double insulated.
I believe the CPC has to also be insulated and sheathed to comply.
I've heard that before in respect of bringing cable into class 2 accessories. Flex is acceptable because the cpc is insulated to the same voltage as the live conductors.
 
The cpc only needs to carry fault current so it’s irrelevant if it’s not sleeved in this case as it’s not classed as a live conductor
 
Try regulation 412.1.1 double or reinforced insulation
Basic protection and fault protection are provided by reinforced insulation between live parts and accessible parts.
Regulation 412.2.

Singles don’t have reinforced insulation so understandably need containment as per regulation 521.10.1,where as twin and earth does, so I’d say it’s not necessarily a requirement to Earth the conduit if metal containing insulated and sheathed cables
Insulated and sheathed cables do not provide either double or reinforced insulation. They merely provide mechanical protection.
 

Reply to Bonding of conduit in kitchen floor in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock