- Reaction score
- 2,580
Not necessarily. There are plenty of all metal class 2 light fittings around.
I was waiting for that one.
I'll put it another way. Name a good reason not to earth it.
Discuss Bonding of conduit in kitchen floor in the UK Electrical Forum area at ElectriciansForums.net
Not necessarily. There are plenty of all metal class 2 light fittings around.
We are not talking personal preference, we are saying is it a requirement of bs 7671I was waiting for that one.
I'll put it another way. Name a good reason not to earth it.
It's in a kitchen , a chance of wet floors + it gets wet and becomes live !common sense dictates that if it's metal, contains wires and could be touched then it should be earthed.
No need palThat was my point but you made it in a much less smart arsey way.
I blame too much paperwork.
my apologies to Ian for said smart arse manner.
T&E does not have reinforced insulation it has one layer of electrical insulation and an overall sheath which provides protection for the electrical insulation.Try regulation 412.1.1 double or reinforced insulation
Basic protection and fault protection are provided by reinforced insulation between live parts and accessible parts.
Regulation 412.2.
Singles don’t have reinforced insulation so understandably need containment as per regulation 521.10.1,where as twin and earth does, so I’d say it’s not necessarily a requirement to Earth the conduit if metal containing insulated and sheathed cables
There are exceptions to the requirement to Earth exposed-conductive-parts. One of which is where the wiring system is deemed to be double insulated.
Thanks. So 410.3.9 negates 411.3.1.1 as long as 412 is satisfied. Next question for me is does twin and earth satisfy 412 as double insulated ?410.3.9.
I've heard that before in respect of bringing cable into class 2 accessories. Flex is acceptable because the cpc is insulated to the same voltage as the live conductors.On second thoughts, I don't think T&E does satisfy the requirement to deemed double insulated.
I believe the CPC has to also be insulated and sheathed to comply.
Insulated and sheathed cables do not provide either double or reinforced insulation. They merely provide mechanical protection.Try regulation 412.1.1 double or reinforced insulation
Basic protection and fault protection are provided by reinforced insulation between live parts and accessible parts.
Regulation 412.2.
Singles don’t have reinforced insulation so understandably need containment as per regulation 521.10.1,where as twin and earth does, so I’d say it’s not necessarily a requirement to Earth the conduit if metal containing insulated and sheathed cables
Reply to Bonding of conduit in kitchen floor in the UK Electrical Forum area at ElectriciansForums.net