I have a client with what appears to be an intermitent fault on the lighting, but trips the power.

The installation has a 16th edition board with sockets on the RCD side, and lighting on the other side as usual.

Occasionally when the landing light is switched the RCD trips on the socket side. Would a borrowed neutral cause this. The lighting circuit itself has RCBO on it that doesn't trip; does the RCBO have anything to do with it.

I haven't checked for a borrowed neutral on the lighting yet, but even if there was one I can't see why that would affect the other RCD side.

Many thanks in advance
 
Occasionally when the landing light is switched the RCD trips on the socket side. Would a borrowed neutral cause this. The lighting circuit itself has RCBO on it that doesn't trip; does the RCBO have anything to do with it.

When did this fault first occur?

If it occurred immediately after the RCBO was installed then it may have something to do with it.
If it occurred immediately after some work was carried out on the installation that could have created a borrowed neutral situation then it may be that.

If the fault first occurred recently without being obviously linked to recent electrical work being carried out then it is pretty unlikely to be caused by those things.
Borrowed neutrals don't occur on their own, nor do they sit there not causing tripping for months/years before one day suddenly causing problems.
Likewise an RCBO won't sit there for months/years then one day suddenly start causing a different RCD to trip.

What you have described sounds symptomatic of a N-E fault, I'd be carrying out testing for that first off.
 
Well, I’m the second person on this job apparently. Several other electricians from a contractor looked at it 3 years ago. Unfortunately the clients are elderly and it’s difficult to understand what the events and time lines are.

The CU has split neutral bars which I neglected to see previously. So apologies for the red herring there.

I did a wander lead on the hall and stairs lighting to see if there was a borrowed neutral but all appeared OK.

Then I combined all of the lighting circuits into one MCB bypassing the RCBO circuit, but it still tripped.

My last attempt was to temporarily move all lighting circuits over to the RCD side and I thought this had it cracked. But sadly after a while it tripped the RCD.

All IR tests are OK, not outstanding but lowest is 18meg, so I’ve assumed it’s not that.

Now baffled.
 
Have you got an earth leakage tester? You could clamp it and see what leakage is at any given time and ramp test the rcd to see what it is actually tripping at. You could find that it’s close to its limit and turning on a light in that lighting circuit is pushing it over the edge.
 

Reply to Borrowed neutral on split load board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
298
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
357
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms...
Replies
58
Views
8K
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock