Discuss Breaking negative DC twice in disconnect in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Reaction score
0
Hello all,
We have a 175 Kw 1500Vdc string inverter. It has 12 mppt channels with 2 inputs each. Each channel (you can have 1 or 2 strings per "chanel") has 1 DC contactor for the positive and 2 DC contactors for the negatives.
Does anyone know the specific UL requirements for this and where to find it? The requirement being referred to, I believe is breaking the negative twice in a DC circuit. I just cannot find the reference for that.



Thank you!
1 DC+, 2 DC-.PNG
 
Ok, I've looked through my copy of UL508A, there is nothing in it that even references the setup you currently have.

Are you sure that they are 3 separate contactors? I don't see any tag identification on the drawing.

Are you sure they aren't just utilizing 3 poles on 1 standard contractor? This is quite common with DC due to it being more difficult to quench an arc breaking DC current.
 
Rob,
Thank you for your reply and looking it up!

The inverter is an ABB PVS175 - US version. I tried putting in the link but it would not allow.

I think that they were referring to is UL 1699B, UL Standard for safety Photovoltaic DC Arc-Fault Circuit Protection. That reference is used in the technical documents of the inverter. Says that those requirements cover devices rated 1500 volts or less. I do not see where it calls for double breaking but I am guessing this is where it is. I will try to dig more.

In this inverter, there are 12 inputs, so technically there are 3 DC contactors for each input - 1 DC+, 2 DC-. All in the same inverter. These are internal to the inverter. 36 small DC contactors.
I will be able to get in front of one soon to physically see the contactors and circuitry. I have looked at European schematics of the same inverter and they only show one one DC contactor for the negative, so apparently it is resulting from a UL Standard.


Thanks again for your comments!
 
I imagine it is to do with breaking distance. An am wondering if the -ve is connected to the metal chassis of the unit.

Will take a look at the UL standard tomorrow that was posted.

Quite handy being a UL member, unlike the IET, I have access to all their standards for free.
 
Hello all,
We have a 175 Kw 1500Vdc string inverter. It has 12 mppt channels with 2 inputs each. Each channel (you can have 1 or 2 strings per "chanel") has 1 DC contactor for the positive and 2 DC contactors for the negatives.
Does anyone know the specific UL requirements for this and where to find it? The requirement being referred to, I believe is breaking the negative twice in a DC circuit. I just cannot find the reference for that.



Thank you! View attachment 51722
To get the 600 Volt DC rating, 3 poles are typically wired in SERIES.
For grounded PV systems all three poles break the ungrounded wire.
For Ungrounded PV Systems then one Pole breaks the (+) wire and 2 Poles in series break the (-) wire = 3 poles total

Search "Eaton 600 VDC 30 Amp Fusible Solar Disconnect DH161NRK"

1567221114135.png


Features:
  • NEC 690 PV compliant up to 600 V DC
  • UL 98 listed
  • NEC 690.17–compliant labeling warning that the switch terminals may be energized in the open position
  • NEC 690.14.(C) 2 required “PV System Disconnect” label included
 

Reply to Breaking negative DC twice in disconnect in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi, So I'm replacing a small old off grid with a new 7.5kw off grid, & being poor seek best value for my mppt, after long searches I find this...
Replies
1
Views
668
I have been asked/invited to "post more", lol, so let me make another post right away. I thought of sth worthy to post, of interest to many, I...
Replies
2
Views
500
  • Sticky
Ferrets are known for being small, resourceful, and incredibly clever. They can solve many problems by fitting into tight spaces and doing jobs us...
Replies
4
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
522
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock