Colonel Hathi

Hi Chaps
I am about to install an 8.5 Kw electric shower and a 2Kw water heater in a small flat that has a 60A 1361 main suppliers fuse.

The flat has 1*32A ring with 3 sockets, 1*20A radial with 5 sockets and 1*6A lighting circuit with 7 points.
If I allow 2amps for the lighting (at 66%), 40amps for the sockets (100% for the 32A ring and 8amps for the radial at 40%), then 37A for the 8.5Kw shower and 3.2amps for the 2Kw demand triggered water heater (at 40% of 8amps),
I get a total demand of 82 amps.

Am I reading the Time Current Chart correctly?
It seems to flatten out at about 3700 seconds at about 110 amps for a 60amp 1361.
Does this actually mean that it can carry 110 amps for 58 minutes?
Does it mean that it can carry my 82 amp estimate indefinitely?

Is my 82 amp estimate actually reasonable in the real world?
I cannot imagine that 8 sockets and 7 lightbulbs would really pull 42 amps?

Any advice is much appreciated.

CH
 
Last edited by a moderator:
Quit worrying, you'll not see anything like your calculated loadings. Those diversity formulas (excluding cooker formula) are so way over the top, it's almost a joke!! You'll be very lucky to see 40A for the whole flat!! And that's being generous too!! ...lol!!
 
awnsered your own question, turn everything on and clamp meter the live , youl see not up there... some say just take highest breaker and multibly the rest by 0.4

so.. 32+20+6+8 x 0.4 =26A add 37 for shower=63A your shower wont use full current unless youve skin like an elephant... i just know this as a rule of thumb from other posts on thbis forum
 
ther is no hard and fast rule for caculating diversity, and often your own knowledge of the installation in question will give more accurate figures than any calculation. Ive never seen a ring final in a house pull 32A. the 8.5kw shower will only pull 37A a) if your voltage is at exactly 230, and b) if it is working at full power. In reality,you wont have it anywhere near full power, and you wont have it on for long, so its very unlikely to cause an overcurrent device to pop anyway
 

Reply to BS 1361 Time Current Characteristics in the Australia area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
  • Article
Electrical2Go - Electric Car Charging at Home - Comprehensive Guide As EV ownership and the transition towards electric cars rise, having a home...
Replies
0
Views
118
Hi everyone. A DIYer here, not looking to fix this issue (as the house in question is hundreds of miles away...) but to try and help owner to...
Replies
15
Views
4K
I came across a small electric hot water heater under the sink with a moulded plug in my friend's rented flat. He's on economy 7, and wishes to...
Replies
1
Views
2K
  • Locked
Hi, we need some advice on our scenario with regards to our rewire plan. I will get this out of the way first... We are planning to put the house...
Replies
24
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock