Discuss Bs 60947-2 siemens sirus circuit breakers in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi all.
I've come across siemens sirus bs 60947-2 circuit breakers during a test and inspection job.
I can't find any info on its breaking capacity and also its maximum permitted Zs.
Any help would be much appreciated.

Len
 
As above, you need to find the unit's data sheet as MCCB and related motor control protection, etc, are all pretty much manufacturer-specific details.

As a pointless exercise I searched for Siemens Sirius range and found an example part 3RV2331-4PC10 in the range and this is the current page:
Getting the data sheet (click on "DataSheet in PDF" and download it) it shows the "response value current of instantaneous short-circuit trip unit" (i.e. the "instant trip") as 520A.

Assuming 230V/400V 3-phase then the max cold-measured Zs would be:
Zs = 0.8 * 0.95 * 230V / 520A = 0.34 ohm

Obviously you need to repeat this with the real part(s)!
 

Reply to Bs 60947-2 siemens sirus circuit breakers in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone I bought the following device for the purpose of inspection and testing of DPs and its connecions...
Replies
7
Views
733
Background Two weeks ago, lightning struck a tree in our yard. Many circuits tripped and several electronic devices failed. There was a strong...
Replies
2
Views
864
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
845
I recently had my 50yr old 100A main panel replaced with a 200A Siemens panel (MC2040B1200EFC). It is the incarnation with the 200A main breaker...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock