You really need the data sheet for MCCB as they are not as standardised as MCB or BS88 fuses. Also for any adjustable MCCB you need to take in to account the settings in use.

Merlin Gerin are now part of Schneider so it is probably worth asking their technical help line for the info.

As a rough guide MCCB are often comparable to D-curve MCB, hence quite a low Zs if you need to meet 0.4s final circuit ADS.
 
You really need the data sheet for MCCB as they are not as standardised as MCB or BS88 fuses. Also for any adjustable MCCB you need to take in to account the settings in use.

Merlin Gerin are now part of Schneider so it is probably worth asking their technical help line for the info.

As a rough guide MCCB are often comparable to D-curve MCB, hence quite a low Zs if you need to meet 0.4s final circuit ADS.

Thanks for your reply. I've spoken with Schneider and they have informed me that the BS number is IEC947-2 which I believe is the equivalent of BS EN 60947-2.
They have also provided me with a table for max Zs for compact range of merlin gerlin. Due to the age of these MCCB's there is limited data they can provide me.
Only issue is the C161N range MCCB doesn't show D63a Zs, however it does show D80a at 0.36. If I can achieve 0.36 or less, then in theory a D63a would have a higher max Zs anyway. This is my thinking correct me if I'm wrong.

I'll attach the file if this helps anyone else after max Zs for merlin gerlin compact range.
 

Attachments

  • Zs Values Compact C.pdf
    168.7 KB · Views: 12
Thanks for your reply. I've spoken with Schneider and they have informed me that the BS number is IEC947-2 which I believe is the equivalent of BS EN 60947-2.
OK good to hear!

They have also provided me with a table for max Zs for compact range of merlin gerlin. Due to the age of these MCCB's there is limited data they can provide me.
Only issue is the C161N range MCCB doesn't show D63a Zs, however it does show D80a at 0.36. If I can achieve 0.36 or less, then in theory a D63a would have a higher max Zs anyway. This is my thinking correct me if I'm wrong.

I'll attach the file if this helps anyone else after max Zs for merlin gerlin compact range.
It seems the 125 frame has virtually the same Zs for 100A & 125A versions as the 161 frame, so it would be reasonable to assume the 63A version of a 161 frame MCCB would be similar to the 125 frame 63A = 0.4 ohms / 0.55 ohms. But for sure no lower Zs than the 80A one tabulated!
 

Reply to BS number/ Zs MCCB help? in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi everyone, Happy Friday! Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve...
Replies
4
Views
1K
Hi everyone, Happy Friday! Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve...
Replies
0
Views
855
Hi All, We have a Merlin Gerin Compact NS100N Single Phase MCCB I've been asked to find its Max ZS Values and to be honest I cant find anything...
Replies
6
Views
3K
Hi All, As ever another question regarding Max ZS! I just need help reading these curves and getting my head around them. Data sheets confuse me...
Replies
0
Views
1K
Hi Guys Changing my heating/water programmer and im stuck on the wiring ive gone from a danfoss to a Drayton and the wiring description is...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock