Discuss Bs7671 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
5
I seem to remember when in college a rule for when using the figures within the BS7671. It was something like divide by 0.8 rule of thumb to certain figures to allow for temperature considerations. As figures in bs7671 and the on-site guide differ slightly. Can anyone elaborate on this and explain it to me please?
 
on table 41.3 they give you the uncorrected (tabulated) figures. to correction factor, you have to mutliply the bs7671 figure by 0.8. this is the max Zs allowed on the circuit.

eg type B 32amp bs7671 = 1.44 ohms

final with correction factor - 1.44 x 0.8 = 1.152 ohms
 
the osg figures are the BS7671 values x 0.8. i dispute the osg values for most applications as when does a cable ever run at 70deg?
 
I suppose its for the worst case senario. Excess load on the cable so the protective devices would still operate??
 
yes. your measured values should be below the tabulated max. values, unless it's TT earthing with RCDs used for fault protection. then the max. is 1667 (for 30mA RCDs)
 
there's 450+ pages of little things like that in BS7671, but not all are relevant to the job you're doing.
 
like playing all the right notes, but not necessarily in the right order (eric morecombe)
 

Reply to Bs7671 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, my name is Pete and I’m new to this site. Could anyone clarify the following question for me please. Does BS7671 cover rules on...
Replies
7
Views
888
Hello All. I am taking my 2396 written exam in December this year, therefore i am knee deep in practice papers. In case anyone else is in the...
Replies
8
Views
1K
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Replies
10
Views
2K
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
Hello, I took the opportunity over the lockdown to do 18th Ed course but theres a few bits im struggling with. Because its distance learning, the...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock