Discuss Cable de-rating for trunking in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
55
Just doing a re-wire on a community hall/scout hut. There's a actually a surprising amount of cable gone into a 25 x 10 m one storey building. 6 x 3kw heaters, sockets everywhere, water heaters , LED Panels, downlighters etc etc.

All cable runs are being done in the loft space and due to the shape of the building and the location of the meter all start by running along one wall before heading out along the ceiling joists.

In an effort to tidy this up and prevent damage to cable I've put everything on that side into 100 x 50 mm trunking. As the rest of the install is clipped direct should I be worried about the cable grouping de-rating factors?
 
Should you be worried? No, not in the slightest. Should it be something you take in to account? Absolutely.

It's worth remembering that the appendices in BS 7671 after 1 are only informative. Also worth remembering is the fact that when it comes to the grouping factors shown in appendix 4, these only apply to cables under prolonged and steady-state operation at 100% of load factor.

If you as the designer decide that after taking this into account certain derating factors need to be applied so be it. If not, so be it.

This is a call you and you only can make as none of us here are the ones designing the installation.

All I will say is that nine times out of ten, when grouping factors have been applied, they're normally wrong, and grossly overcalculated.

That being said, my advice should not be taken as carte blanche to sling cables together willy nilly without a care in the world.
 
Grouping factors can be ignored for cables if cables are carrying no more than 30% of it's grouped rated current.
It's worth remembering that it's the amount of circuits which contribute to the grouping calculations not the amount of cables present.
As already pointed out it's your call.
 
I should of read the post properly sorry it is just the run from the distribution board, I think it will depend upon the length to which there will be a detrimental effect on the cables CCC and grouping factor needing to be applied ,however assuming if the cables are run in the loft space they will be in contact with insulation and be de-rated/CCC increased therefore you will need to see which one is the more arduous condition. I would go for 100 x 100 trunking (there would be no reason why you could not fit cable spacers inside the trunking to reduce grouping factor).
 
Especially if it was a 100x100 room for spacing and a little bit of dancing too! One gets hot when one dances, no different with cables and electrons!
As all the cables would not be grouped in all one lump together
 

Reply to Cable de-rating for trunking in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
850
Hi. I am planing on building a (not sure what to call it) U shaped storage solution which goes either side and above the headboard of a bed. I...
Replies
12
Views
4K
Hi My consumer unit is located in the garage, the cables are currently clipped to a solid wall above the unit. I am considering putting the...
Replies
18
Views
6K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Im Working on a new build site at the moment, and the kitchen layout has changed to include an island with a hob on it. Meaning im goin to have...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock