Hi
Has anyone had any experience of excavating to find HV underground cables in CBS backfill? I am being asked increasingly to use CBS (usually about 1:14 Cement/sand) for bedding and cover infill of cable ducts we install. Reason usually given is that apparently it helps with heat dissipation in some soils and presumably also helps stops warning marker tapes being able to move away from the duct with any soil settlement.
I am concerned that it may not be possible to use hand tools to excavate to get to the cable to prove dead/spike it if further work is required on the circuit later on. As I have never tried to break any out in the past, will it break up or come away with gentle use of a spade or grafter or does it go off quite hard?

Any advice gratefully received
Mark
 
Yep,it breaks up easy,i have had to rip up loads round here,as a similar mix was specced as bedding for vehicle use paving flags (3x2 and 2x2) on and around some local LA offices.

The main reason for it's use,was not load bearing,it was ability to resist under-cutting by water and ants! The LA still spends a considerable amount,spraying all the footpaths locally,for the ant issue.

A consistent mix,at similar ratios to above,will be removable using hand tools,but the problem is always consistency. The lads hoying it in,have a lot to mix,and figure it has no importance,so be prepared for the odd tungsten nugget...

It is only the same as pricing breaking out a large concrete slab,and finding the ground workers disposed of the surplus 2 Cu of concrete,by trebling the depth of the last section...Thank you Lever Bros :(
 
We sometimes use a soil cement mix in cable trenches to deter moles and porcupines from digging up the cables. The soil here is very sandy, not like your UK soil and we generally use a 1;20 cement ; soil mix by volume. When it's fully set it's pretty crumbly and can easily be broken up with a spade
 

Reply to Cable Duct install in Cement Bound Sand (CBS) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi Everybody Has anybody on here any experience of using a Bosch GMS 120 cable detector? The scenario I have is that I am working on a stone built...
Replies
1
Views
2K
"Hello All", I am trying to find out some information to give to a Friend who is investigating the cause of Damp in his Home`s wall and has seen...
Replies
55
Views
11K
Geordie Spark
G
J
Hi Guys I am hoping to get some outside opinion on an installation that I don't think is safe but others do, I've drawn a shocking pic which I...
Replies
32
Views
3K
Last week I did a job for forum member joramtor. Link to the original post here...
Replies
112
Views
13K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock