gerard

Hi,
Just wondering if anyone knows of a gland for protecting a cable through 6-8mm thick metal? I could drill and tap ordinary glands but I have loads to do and looking for easier option. I am considering using bushings but would prefer thight fitting gland
Cheers
 
You should be able to order extended reach glands from Hawke or CMP (not sure if other makers do them, but probably they will) with a 25mm thread as opposed to 15mm.
 
If you have a load to do and its just for protection through a steel plate, have you considered using a transit frame and blocks ? On a standard 6x1 frame you can get some 48 cables of 15 mm diameter, or 24 of 24mm diameter. Otherwise if its a termination entry then you may need to consider some form of earthing the cable armouring if applicable in the enclosure (constant force springs and earth wire for example).

MCT Brattberg - Installations
 
Last edited:
Hi,
Just wondering if anyone knows of a gland for protecting a cable through 6-8mm thick metal? I could drill and tap ordinary glands but I have loads to do and looking for easier option. I am considering using bushings but would prefer thight fitting gland
Cheers

I suppose this is a silly question, but why don't you try a long reach bush and a coupler?

I think it would be the easiest and cheapest way of doing it.
 
I didn't want to use a bushing because I wanted a tight fitting that a gland gives. The machine in which the cables are located vibrates and over time it might wear into cable.
 
I didn't want to use a bushing because I wanted a tight fitting that a gland gives. The machine in which the cables are located vibrates and over time it might wear into cable.
in that case you could use a flanged bush with a lead washer (they come with a long-reach bush)

I worked on a fisheries protection vessel in shipyard in North Devon.
terminating 2x star-delta motors just outside the engine room, I found that the gland plate was about 10mm thick.
The first hole I drilled in at the motor.
The other 3 I drilled on a pillar drill in a workshop.
I know there is alot of vibration in 38 meter Naval vessel and it was acceptable there.
 
The cable was connected to a motor that moves and I was concerned about the constant movement. Observed it working and it seems fine. All good now thanks!
 

Reply to Cable glands for thick metal sheet in the Canada area at ElectriciansForums.net

Similar Threads

Hi All. What is the best/preferred method when connecting 20mm conduit to a back box of a socket on an outside wall ? I am connecting a BG...
Replies
10
Views
3K
Hello I’m going to install a hard wired 230v security camera, incorporating floodlights, outside and above garage door onto brick. An exposed...
Replies
1
Views
968
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
558
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Replies
7
Views
2K
A friend of mine is looking to have an electric shower fitted and has floorboards up already (mostly, long story). Anyway there is a run of 2.5mm...
Replies
32
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock