Reaction score
4
Found two 25m cable reel extensions on a pat test yesterday with no RCDs should they be automatically taken out of service. They were at least 10 years old. The 5th addition says up to 15m max?
 
You can get extension reels in all sorts of length I see Screwfix selling a 45m one, from a reputable supplier. We have a rule of thumb that where the earth bond exceeds 0.18 ohm (I believe this equates to the suggested lengths in the CoP) that it is recommended it is only used with 30ma rcd protection, of course this does not take into consideration any volt drop issues.
 
You can get extension reels in all sorts of length I see Screwfix selling a 45m one, from a reputable supplier. We have a rule of thumb that where the earth bond exceeds 0.18 ohm (I believe this equates to the suggested lengths in the CoP) that it is recommended it is only used with 30ma rcd protection, of course this does not take into consideration any volt drop issues.
Unwound the 25m reel was failing at 0.56 ohms. Before I started doing the maths to check !
 
Your tester probably has a default setting and sees the earth bond reading as too high when in fact it is just the nature of reels length.
 
What tester are you using? Some have settings for different length reels or a setting to put your own pass/fail value in if it's an odd length reel.
 
You can't take them out of service for not having RCDs. The socket feeding them will more often than not have RCD protection.
 
Are you talking about the RCD on the DB ??? They’re certainly not using a plug in RCD.

But it's an extension lead, not a permanent bit of wiring. Can be plugged into any 13A socket.
 
Sorry, I've just realised the length of cable is your issue. I ignored that bit in my rush to read it. I'll dig out my code of practice and remind myself what it says.

I'm pretty sure you're right though. Isn't it over 12m they need to have a built in RCD?

Haven't got the 5th edition yet, not sure if anything has changed in that. I suspect not.
 
It's not always the same figure. It's 12, 15 or 25m depending on csa of cable.

See table 15.4 of code of practice.
 
13A fuses have Zs limit of 2.3 ohms (Table 41.2) so assuming your supply Zs is around 1 ohm at the socket then if your cable R1+R2 is 1.3 ohm or less no problem?
 
13A fuses have Zs limit of 2.3 ohms (Table 41.2) so assuming your supply Zs is around 1 ohm at the socket then if your cable R1+R2 is 1.3 ohm or less no problem?

They do give specific limits on length in the ISITEE code of practice though.
 

Reply to Cable reels pat testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
674
Hi, I perform annual PAT checks for my company (office and workshop). The Apollo 400 machine we use has recently gone for calibration and service...
Replies
7
Views
883
Hi all, Testing question for you. I'm currently testing an existing domestic installation. The wiring is about 20-25 years old. We have rewired...
Replies
7
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
274

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock