Discuss Cable size in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1,228
Hi,

I am going to be connecting an out door power supply, away from the building, its all metal casing.

The supply is 10mm, I am using a 3 core SWA for part of the run, the inside part was going to be in twin and earth, but then I was just thinking, going on table 54.8 section 544.1, am I looking into this too much or does it need to have a 10mm earth as its extraneous metal which is fixed into the ground?

In which case I was just thinking of running 3x 10mm inside the building so the earth is 10mm too to them comply with min size of bonding conductor.

I am right to make it 10mm throughout the entire run aren't i?
 
are you saying that the outbuilding is metal construction? if so, earth the SWA armour at house end but then TT the outbuilding.
 
No its not a building, its a free standing post on a metal ground mount kit bolted into a concrete pad in the ground, all metal.

Its a commercial property / warehouse.
 
Your Bonding size in that case depends on the size of the incoming Neutral, not necessarily the tails size, depending on type/location, length of run and where the remote part is situated, a remote TT might be a consideration to take into account

Edit: beaten by Tel :)
 
hmm. new one to me. let's see what other minds think. the 10mm sounds like a way forward.
 
its a three phase incommer with 25mm from each and the neutral is 25mm.

I think ill just run some SY inside as thats all 10mm then, I wonder if that will leave me a problem crimping the SY to the SWA...
 
Why not just run SWA all of the way? There's no sense putting a joint in a brand new cable if it can be avoided.

And as for SY, i'd say it's probably not the best choice. Unless this circuit needs electromagnetic shielding, but then SWA won't be any good if it does.
 
So what made you select SY for this job? Why does it need an electromagnetically screened flexible cable designed for control circuits and according to manufacturers data sheets should not be connected to the public electricity supply?
 
Well it was really just an easier way of getting 3x 10mm in one cable, but am just thinking of alternatives now as the run needs to be 16mm, not 10mm, thats my fault, I was basing it on the original loading.

So will rin 16mm SWA to adaptable box, then from there to the dist board I am not sure yet.
 
So what made you select SY for this job? Why does it need an electromagnetically screened flexible cable designed for control circuits and according to manufacturers data sheets should not be connected to the public electricity supply?

What would your preference to running 16mm line and neutral and a 10mm earth for 9 meters in some basket be then?
 
16mm 3core SWA

Normally that would be my choice too, but its just not really possible, ill just for 16mm twin and a 6mm earth, thinking about it, it doesn't need bonding anyway as its outside the equipotential zone. Im just being thick. it needs earthing, but not bonding.

Ill just work out the fault current and see, but im sure 6mm will be fine.
 
New posts

Reply to Cable size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
335
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
745
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
776

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock