Hi all, I know it's hard to tell without seeing a job but, we're wanting to put some camping pods in at one of our sites. We're only looking at basic electrics, LED lighting and a couple of sockets for phone charging but no heaters as they won't be used all year round. We considered 16A caravan hook up points but I think we'd rather wire them direct. There will be 5 of them at 16A so total load would be 80A and the length of cable will need to be about 140metres. The cable will be SWA buried underground. Someone said they had worked out that the cable size would need to be 35mm because of the voltage drop on that length of cable, it seems kind of big to me but it's not my area so thought I'd ask those in the know. Thanks
 
There will be 5 of them at 16A so total load would be 80A and the length of cable will need to be about 140metres. The cable will be SWA buried underground. Someone said they had worked out that the cable size would need to be 35mm

Multicore 90°C Armoured Thermosetting Insulated Cables​

Tables Apply to: H6942XL, H6943XL, H6944XL, H6945XL, Tuff Sheath,

Voltage:230V

Load:18.4kW / 80A

Length:140m

Method of Installation direct in ground or in ducting in ground

Cable Size:50mm²
 
I’d advise getting an electrician involved. They will know to add diversity to your calculation, which means your 16A times 5 pods won’t actually need 80A

You say no heating, but what about appliances that heat, such as kettles?
Without any high load, and it’s just lighting and chargers, tv, etc…. They won’t pull 6A never mind 16
 
I would be more inclined to install 3 phase supply if available and tap of phase and neutral per hook up point you could use 16mm and still have scope for additional load should it be required
 
And also it's a distributed load, so only the incoming section of cable takes full load, and each sequential section takes correspondingly less. Does reducing cable size along the run help cost, or just complicate the job?
 

Reply to Cable sizing for camping pods in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Replies
5
Views
668
Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
907
Got an EV (Nissan Townstar EV) in my house, has a Zappi EV charger installed (by myself) and notified via ENA form to Scottish Power energy...
Replies
4
Views
1K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
571

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock