Discuss Cable Type in the UK Electrical Forum area at ElectriciansForums.net

As mentioned,possibilities of issues are many...but inspection and testing of said circuits should not be discounted.
I have encountered, VIR that neither fell apart,nor failed testing,and in such a circumstance,replacement would be recommended on the basis of unknown service-life expectancy.

Or,sometimes,just shaking your head,whilst the customer looks on,and saying "This is older than me mum..." can do the trick :)
 
That's not VIR, it's a TRS (tough rubber sheath) twin or twin and earth cable, it is made of a natural rubber and used in the 1950/60's era. It will now be past it's service life and due for replacement.


VIR is, or was only ever used to describe, the single core cables similar to the singles used in conduit installations today.
 
The cables with a title of "tough rubber sheathed",can still have a composition of vulcanised india rubber,in the sheath or insulation. It depends on the age of the cable.

Modern TRS cables,such as produced by Doncaster cables,use a cross linked elastomeric compound,in the sheath,but confusingly,use a product description,of "VR insulated tough rubber sheathed" for their current stock.

If anyone has two drums of the original stuff,one scrap,and one untouched....it'll be Lucien :)
 
The cables with a title of "tough rubber sheathed",can still have a composition of vulcanised india rubber,in the sheath or insulation. It depends on the age of the cable.

Modern TRS cables,such as produced by Doncaster cables,use a cross linked elastomeric compound,in the sheath,but confusingly,use a product description,of "VR insulated tough rubber sheathed" for their current stock.

If anyone has two drums of the original stuff,one scrap,and one untouched....it'll be Lucien :)

Interesting. The insulation in the black rubber sheathed looks very similar to that of the waxed cloth covered singles when I have encountered them both before. Thankfully not seen much of either still in service.
 
The customer is a mate who is planning to sell the house so a rewire is not really on the cards for him, I have told him that it needs a full rewire, new consumer unit etc and that as and when he sells it this will probably be picked up on a survey. It is a TT and has no upfront RCD so fairly crap all round, the question is does he want to spend the money or reduce the price if picked up or leave it to the next occupant. The interesting thing is a local ELECSA installer recently did some work for a new kitchen by putting a 10mm feed to a small consumer unit with a stand alone RCD for that cable only, they put in a new earth rod and used a bonding strap to fix it leaving it about 8" out of the ground and not in an earth pit, a right dogs dinner!
 

Reply to Cable Type in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Had a customer message me before I went to do a job asking if I could put a new bulb in a spotlight while I was there, so I picked up some LED...
Replies
5
Views
378
Hi All, Im quoting to install an EV charger (Dont worry - fully registered, but only been 2 weeks so i'm still picking bits up). Consumer unit...
Replies
1
Views
1K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
819
Hi guys, I don’t really know where to post this, sorry if it’s in the wrong place. After posting a thread about old lead sheathed cable in my...
Replies
22
Views
2K
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
851

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock