Discuss Cable visible through plaster in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
73
Was doing an EICR and came across this issue was unsure how to code it, a couple sockets within the kitchen area you can see the sort of outlining of the T+E cables in the plaster going up to the sockets. It’s RCD protected but it’s just a bit poor
 
Without knowing how it was agreed the cables should have been installed then I'm not sure it warrants any code.

Surface cables are allowed, buried cables are allowed, half in/half out whilst unsightly is not non-compliant for an old installation.

Now if it was brand new they would need RCD protection.

But it could have Ben a case of 10mm of plaster on a granite stone wall, the customer may have been quoted to chase out but baulked at the cost.
 
It's not immediately dangerous so not C1.
It's not potentially dangerous so not C2.
It's an example of not meeting fundamental principles of good workmanship, chapter 1 of the regs, so could reasonably be given a C3, improvement recommended.
I've decided to change my view on this, having reread (for the umpteenth time) Best Practice Guide 4.
'Only items that affect the safety of the installation should be recorded.'
So, although not good workmanship, the safety of the installation is not affected, so no code.
 
No code,

However, this could be the sort of situation where the client/home owner could be scared or concerned into thinking the installation is unsafe. They see a cable protruding that they think should be buried and may automatically think it's unsafe.

I might be inclined to perhaps make a little note stating that though the buried cable is slightly exposed, this is perfectly acceptable as there is no potential danger and it has no effect on the electrical system's safety or function. That way at least any concerns are dealt with.
 

Reply to Cable visible through plaster in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
290
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
814
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
For various reasons out of my control, we have wound up in a situation where we have 1.5mm SWA cables buried in these pillars and exiting out of...
Replies
95
Views
7K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock