Discuss Cables with thermosetting insulation (XLPE cables) in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

P

PLW

I understand that XLPE cables operate at a maximum temperature of 90c compared with 70c for PVC insulation. What I don't understand is why the increased temperature permits a reduction in conductor size if XLPE insulated cables are used in preference to cables having PVC insulation.

If the conductor size is reduced the resistance would increase if XLPE cable was used. I understand that the cable has special insulation to withstand the high temperatures, but why is it necessary to reduce the conductor size?
I was under the impression that high resistance and high temperature could potentially be a safety hazard due to the increased risk of overheating as well as having a negative impact on the performance of the cable.

Please can someone explain this. Thanks.
 
xple cable has a higher current capacity so the conductor size can be reduced wrt 70deg. cable. however, as lee pointed out, you must consider the temp rating of any switchgear connected to the cable.
 
The current carrying capacity of a conductor can be dictated by the applied insulation. The temperature of a conductor under load is transferred to the insulation and this must not reach a temperature which can degrade this insulation. Thermoplastic (PVC) will degrade at a lower temperature than cross layered polythene (XLPE) and this dictates its current rating.
Conductors with PTFE insulation will happily operate at 200°C.
 
xple cable has a higher current capacity so the conductor size can be reduced wrt 70deg. cable. however, as lee pointed out, you must consider the temp rating of any switchgear connected to the cable.
why would a higher current carrying capacity mean you'd reduce the size of the conductor ? I thought that for a higher current carrying capacity you'd want a thicker cable to reduce resistance ?
 
why would a higher current carrying capacity mean you'd reduce the size of the conductor ? I thought that for a higher current carrying capacity you'd want a thicker cable to reduce resistance ?
As the XPLE cable can take more current for a given cross sectional area then if you have a specific current you need to carry the conductor size could be smaller for the XPLE insulated cable compared to the PVC insulated cable.
 
The current carrying capacity of a cable is effectively limited by its capacity to dissipate the heat generated in the cable. If the temperature of the cable is higher, then more heat will flow away from it through the insulation and surrounding environment. If more heat can be dissipated (due to the higher operating temperature) then the cable can carry a greater current.
Hence a current carrying requirement that needs say a 6mm cable at 70deg c (pvc) may only need a 4mm cable if it can operate at 90 deg c (XPLE).
 
The current carrying capacity of a cable is effectively limited by its capacity to dissipate the heat generated in the cable. If the temperature of the cable is higher, then more heat will flow away from it through the insulation and surrounding environment. If more heat can be dissipated (due to the higher operating temperature) then the cable can carry a greater current.
Hence a current carrying requirement that needs say a 6mm cable at 70deg c (pvc) may only need a 4mm cable if it can operate at 90 deg c (XPLE).
Much is to do with conductor temperature rise and its effect on the insulation. PVC will deteriorate at lower temperatures than XLPE hence the difference in ccc.
 

Reply to Cables with thermosetting insulation (XLPE cables) in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
491
Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
915
Cathodic Protection Station with Switching Power Supply for Buried Metal Structures Benefits of the Switchmode Cathodic Protection Rectifier...
Replies
1
Views
492
I am self-teaching fault-finding and testing, but I can't wrap my head around insulation resistance tests. From my understanding you send 500V for...
Replies
14
Views
6K
I've just done an insulation resistance test between line and earth and got 0.0 Mohms for most circuits. Obviously this is an F1, but what I don't...
Replies
20
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock