Discuss Calculating the correct cpc size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
1
Good evening all,

Some help with following would be much appreciated.

A 20 Amp rcbo in a CU supplies an adaptable box on the outside wall of a house via 2.5mm2 T & E. From the adapatable box a short lenght of SWA supplies a couple of sockets and light in a shed.

My question is does the 1.5mm2 cpc in the T & E compley with regualtions..?

Given that the cpc is calculated either by using table 54.7 or the adiabatic equation.

Using table 54.7 a cpc of 2.5mm2 would be required.

Using the adiabatic equation S=100, t= 5 seconds, K- 115, giving a cpc of 1.9mm2.

Given that the 1,5mm2 cpc does not comply with table 54.7 or the adiabatic equation, would it be best to use 4mm2 cable or run a seperate earth.

Keep hearing that as a rule of thumb that cpc should be at least half the size of the live conductors but cannot find any reference this in the regs.

Thanks for your help

Chris



 
Where are you getting the 100A current from if the rcbo is only 20A and why are you using a 5 sec disconnection time?
 
Hi - you need to use the prospective earth fault current in the 543.1.3 equation. But, I'd be surprised if 1.5 wasn't ok as CPC for a circuit protected by a BS60898 20A MCB in a domestic situation. However, there may be other issues with loop impedance or voltage drop limits to consider. :)
 
Hi - you need to use the prospective earth fault current in the 543.1.3 equation. But, I'd be surprised if 1.5 wasn't ok as CPC for a circuit protected by a BS60898 20A MCB in a domestic situation. However, there may be other issues with loop impedance or voltage
Hi - you need to use the prospective earth fault current in the 543.1.3 equation. But, I'd be surprised if 1.5 wasn't ok as CPC for a circuit protected by a BS60898 20A MCB in a domestic situation. However, there may be other issues with loop impedance or voltage drop limits to consider. :)

Hi Thanks for the Replies,

20A rcbo max zs is 2.19. porospective faut current is 105 A. 5 seconds for T as it is a distrubution circuit. puting these figures into the equation gives a cpc of 2.04mm2 far too high i think.

Will have another look at the equation tomorrow evening.

thanks again


drop limits to consider. :)
Hi - you need to use the prospective earth fault current in the 543.1.3 equation. But, I'd be surprised if 1.5 wasn't ok as CPC for a circuit protected by a BS60898 20A MCB in a domestic situation. However, there may be other issues with loop impedance or voltage drop limits to consider. :)
 
Hi everyone, thanks for the replies.

Max zs for a 20A rcbo is 2.19, giving a fault current of 105 A, 230/2.19.Using 5 seconds for t as it a distribution circuit, think this is where i'm going wrong. K =115.

Putting these figures into the equation gives a cpc of 2.04, far too high i think.

Will look at the equation again tomorrow evening.

Thanks again
 
Hi everyone, thanks for the replies.

Max zs for a 20A rcbo is 2.19, giving a fault current of 105 A, 230/2.19.Using 5 seconds for t as it a distribution circuit, think this is where i'm going wrong. K =115.

Putting these figures into the equation gives a cpc of 2.04, far too high i think.

Will look at the equation again tomorrow evening.

Thanks again
I would class that as a final circuit unless of course there is another over current protective device at the juncture between the t&e and the swa which I would doubt if they are joined in an adaptable box.
 
Whether it's a distribution circuit determines the required disconnection time which would let you decide the protective device.
you would then use the actual disconnection time when using adiabatic to calculate the i2t.
This could be based on the PEFC if the ze is high enough to prevent magnetic tripping, or it could be looked up from the let through for the upstream protective devices for low ze.
Either way, for a 20A type B with a 125A or less bs88 fuse, 1.5mm will always be enough.
 
Max zs for a 20A rcbo is 2.19, giving a fault current of 105 A, 230/2.19.Using 5 seconds for t as it a distribution circuit, think this is where i'm going wrong. K =115.
Hi - to work out CPC sizing we need the PEFC at the source of that actual circuit, not the minimum needed to get ADS. Thats because the fault could occur adjacent to the breaker. Edits with thanks to JD :)
 
Last edited:
Hi - to work out CPC sizing we need the PEFC of that actual circuit, not the minimum needed to get ADS.
Agree although to be clear it's the pefc at the circuit origin. and in fact as above the minimum to comply with ads on a distribution circuit is 5 seconds, regardless of whether the protective device has a magnetic trip.
So in the ops case it would be well under 100A, which would be interesting to put through adiabatic but should still come out below 1.5mm
 
Thanks again for the replies.

From fig 3A4 the current that would cause a 20 A rcbo to trip in 0.1 to 5 seconds is 100 A
T = 5 Seconds (distrubution circuit)
K =115

Putting these figures into the adiabatic equation, I get a minimum cpc of 1.9 mm2

Could someone please advise if i have used the correct figures in the equation to get a cpc of 1.9mm2

Thanks for your help
 
And I still can’t see why it’s a distribution circuit? Apologies if I’ve missed something
Hi - I'm too sure what's proposed here exactly (lm a bit worn out tonight) but if there is current using equipment attached to this 2.5mm cable directly (lights, outlets etc) then it's a final circuit. If it only feeds another board, then it's a distribution circuit. But at 2.5mm it's a bit anorexic :) .
 
Op only states it’s 2 sockets and a light, I assumed he was fusing down the lighting point,which makes it a final circuit so disconnection time 0.4?
OP I am reasonably new to this myself so if I’ve quoted anything wrong I do apologise
 
I'm not sure the OP understands why the equation exists and what exactly it's trying to prevent. Basically in simple terms it's preventing a high current of short duration from damaging the cable insulation.

The energy per metre of the cable is what heats it and the volume is what buffers the heating due to thermal mass. I.e. twice as much copper takes twice as much heat to get to, say 100c.
This is measured as a constant number of joules "j" per cubic metre of copper required to heat the conductor by the required number of degrees. j joules per metre^3
This is the same as j watt seconds per metre^3
or j volt amp seconds per metre^3
or j ohm amp amp seconds per metre^3.

The resistance of the cable (ohms) is proportional to the length (metres) so we end up with amp amp seconds per metre^2 times another constant "r". Let's make a new constant "k" which is just r.j From that blurb we just derived the adiabatic equation:
CSA = k (I^2)t.

So what is I? the actual current that will flow in the worse case, an earth fault at the origin? ie. the PEFC.
So what is t? the time the current will flow before being cut off. You can read that from your protective device chart. Make sure you read the worse case, not the average.
Can't read t because the disconnection time is less than 0.1 seconds? There is another protective device chart, you have to check the energy class of the MCB, and look up based on the upstream protection. Then you can just read the I2t straight off the chart.
 
Hi Chaps,

Just been reading the thread. There seems to be some confusion.

The maximum disconnection time is 0.4 seconds. As it classed as a final circuit and is under 32A. See reg 411.3.2.3

You need the Zs of the circuit. That is the Ze +R1 +R2 for the length.

Then calculate the fault current. The nominal voltage 230/Zs = If

Then you need to check the disconnection time from the protective device curve, or the associated table on the curve figure. t

Now you can do the adiabatic equation.

S = minimum cpc size
If = the result of the above calculation
t = disconnection time from the figure
K = the constant for copper 115

Don't forget the squaring and square rooting. I think you maybe surprised how small the cpc can be calculated to.
 

Reply to Calculating the correct cpc size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
801
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Hi all, I have been asked to install individual three-phase supplies for a band saw and table saw. Having trouble figuring out the correct cable...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock