Discuss Calculating volt drop in the UK Electrical Forum area at ElectriciansForums.net

TJC1

-
Reaction score
6
When doing volt drop calcs, should you use the rating of the mcb/rcbo for the design current or the realistic current the circuit is going to use?

Just doing a calc for 40m or 4.0mm 3core swa feeding 6 sockets. Im going to wire them in a radial via b32 rcbo
 
I agree design current, but I usually do the max possible loading also just to check.

I then inform customer of results saying “this cable size is fine for the load information you have supplied, but if you use the max load the breaker can supply the volt drop would be....”

Either fine or not.

The customer then sometimes come clean with what the actual loading could be if the volt drop is not acceptable at the higher load. Quite often customer will request larger cable size.

Not Necessary, but good practice.
 

Reply to Calculating volt drop in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
407
Im currently in my apprenticeship and completing an assignment that involves cable calculations. Im currently stuck on how to find the design...
Replies
1
Views
573
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
1K
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
925

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock