Discuss Volt drop calculation on spurs off of a ring. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hello,

New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit but am getting confused when in comes to incorporating a spur and and just wanted some help to confirm if I am calculating the volt drop at a fuse spur correctly or not. The ring is approximately 17.2M and there are 3 13A fuse spurs totalling 0.6M each in length (not included in length calculation for ring)

I have calculated the volt drop of my ring without the 13A spurs as followed...

Length – L
Mv/A/m
Volt Drop (Ring)
Max Volt Drop
17.2M​
18​
18 x 32 x 17.2 / 4 x 1000 = 3.99V​
5% (11.5V)​


Length – L (Spur)
Mv/A/m
Volt Drop (Spur)
Max Volt Drop
0.6​
18​
18 x 13 x 0.6 / 1000 = 0.14V​
5% (11.5V)​

Is this the correct way of calculating the volt drop of the spur by adding the volt drop of the ring to the volt drop of the cable to the spur = 4.13V?
 
You have done the calculations correctly for the worst-case of both a fully loaded RFC along with a spur at maximum load.

Realistically though unless the spur is really long it can be ignored as often the RFC is below max load, the spur is not at mid-point (max VD) and well within its own max current and so voltage drop limits.

Being able to understand and perform the calculations is necessary for many cases where you have odd loads but for the vast majority of RFC applications then as long as the length falls within the limits given in the On-Site guide (Table 7.1(ii) on page 75 of the 18th AM2 OSG) you are OK.
 
Just to add that generally speaking I don't like spurs off RFC as they break the excellent end-end test that all CPCs are connected, etc. However, from what you describe above it is probable a few unswitched 13A single sockets off 20A isolator switches for kitchen white goods where such an approach makes a lot of sense. In fact the Scottish building regs demand accessible isolation for such white goods.
 
Last edited:

Reply to Volt drop calculation on spurs off of a ring. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
Replies
12
Views
7K
I'm getting a little confused about volt drop and 24v. I want to fit an LED strip light. 8m of lights 7w/m. It would be easier to have the 24v...
Replies
13
Views
5K
Hi, I am a DIY person (ie. not a qualified electrician) so I am sure this is a basic question but please bear with me. I am looking to add a...
Replies
6
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock