fire8789

Hi Guys, I'm fairly new to the industry and have sat and passed all the relevant exams to become a Domestic installer. I'm a little stuck with one of my pieces to be assessed by NICEIC. I'm doing a full rewire at my dads house and would like to check that I'm calculating the cable volt drop correctly.

So for radials it seems to be fairly simple.
(mV/A/m) x Ib x L / 1000

So for a light circuit using 1.5mm 2 core I got
29 mV/A/m x 6 amps x 30meters = 5220 / 1000 = 5.22 volts, so would be ok as it's within 3% (6.9V) voltage drop.

The bit I'm not sure on is how you calculate this for a ring main?

I had a guess here so please let me know if this is correct or would be a suitable method to use?


18 mV/A/m x 32amps x 50meters.

So what I did was to half the Ib ampage to 16A as it's on a ring so the current can be divided between the incoming and outgoing cables, then half the length also for the same reason.
So my formula came to
18mV/A/m x 16amps x 25m = 7200 / 1000 = 7.2v which would be acceptable.

Had I not done this the voltage drop would have been way too high (18mV/A/m x 32 x 50 = 28800 / 1000 = 28.8v).

Help would be much appreciated. cheers. Rich
 
I'm pretty sure volt drop is on radials eg for a supply to a shed. With rings I think (from memory) that's its done on square meterage, which I think is 85 door a ring. Please do correct me anybody though, stuck at a kids party, boring
 
18 mV/A/m x 32amps x 50meters.

So what I did was to half the Ib ampage to 16A as it's on a ring so the current can be divided between the incoming and outgoing cables, then half the length also for the same reason.
So my formula came to
18mV/A/m x 16amps x 25m = 7200 / 1000 = 7.2v which would be acceptable.

Had I not done this the voltage drop would have been way too high (18mV/A/m x 32 x 50 = 28800 / 1000 = 28.8v).
You have arrived at the correct answer so your thinking is good.

However, you should have just divided the total length by 4 (same as for the resistance).

Also, on radial circuits you can use the actual load instead of the mcb rating.
For lighting circuits the v.d. will decrease along the length.
 
Thanks for the replies guys. Table H2.1 seems to be what I had overlooked!
Also cheers for the tip Geoffsd. Might be able to squeeze an extra few meters out of my radial lighting circuit using the design current rather than mcb rating then.
 
Hi Guys, I'm fairly new to the industry and have sat and passed all the relevant exams to become a Domestic installer. I'm a little stuck with one of my pieces to be assessed by NICEIC. I'm doing a full rewire at my dads house and would like to check that I'm calculating the cable volt drop correctly.

So for radials it seems to be fairly simple.
(mV/A/m) x Ib x L / 1000

So for a light circuit using 1.5mm 2 core I got
29 mV/A/m x 6 amps x 30meters = 5220 / 1000 = 5.22 volts, so would be ok as it's within 3% (6.9V) voltage drop.

The bit I'm not sure on is how you calculate this for a ring main?

I had a guess here so please let me know if this is correct or would be a suitable method to use?


18 mV/A/m x 32amps x 50meters.

So what I did was to half the Ib ampage to 16A as it's on a ring so the current can be divided between the incoming and outgoing cables, then half the length also for the same reason.
So my formula came to
18mV/A/m x 16amps x 25m = 7200 / 1000 = 7.2v which would be acceptable.

Had I not done this the voltage drop would have been way too high (18mV/A/m x 32 x 50 = 28800 / 1000 = 28.8v).

Help would be much appreciated. cheers. Rich
Divide the mv/a/m by 4
 
Divide the mv/a/m by 4
(Mv/a/m \4) X IB X L
—————————- = vd in a ring
1000

you 1/4 the mv/a/m figure because it’s a ring.

Ib can be the mcb/rcd size eg 32a
Or 26amps because that’s a rings design current in the on site guide.
What I’ve used below.

(18/4= 4.5) x Ib x L
—————————
1000

4.5mv/a/m x 26amps x 50 meters
_______________________________ = 5.85v
1000
 
(Mv/a/m \4) X IB X L
—————————- = vd in a ring
1000

you 1/4 the mv/a/m figure because it’s a ring.

Ib can be the mcb/rcd size eg 32a
Or 26amps because that’s a rings design current in the on site guide.
What I’ve used below.

(18/4= 4.5) x Ib x L
—————————
1000

4.5mv/a/m x 26amps x 50 meters
_______________________________ = 5.85v
1000

Just to note, he's not been on for 10 years.
 

Reply to Calculating Voltage Drop on a Ring main in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
817
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
844

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock