Discuss can a consumer unit switch be replaced by an RCD? in the DIY Electrical Advice area at ElectriciansForums.net

alanma

DIY
Reaction score
0
HI
My flat just failed the EICR because there is no RCD in the consumer unit.
There is no space for a new RCD as the consumer unit is full.
Do I have to have a new larger consumer unit installed?
Or can I have the existing on/off switch replaced by an RCD?

Thanks
Alan
 
Hi Brian thanks for responding, can you tell me what selectivity is in this con
text?
Many thanks
Alan
 
Hi Brian thanks for responding, can you tell me what selectivity is in this con
text?
Many thanks
Alan

If you have one RCD covering the whole installation then any earth fault will result in loss of power (including lighting and fridge) to the whole house.

Also, all circuits naturally have some amount of earth leakage. If all circuits are fed from one RCD then this total leakage figure may be enough to trip the RCD, even though there is no actual fault.
 
If you have one RCD covering the whole installation then any earth fault will result in loss of power (including lighting and fridge) to the whole house.

Also, all circuits naturally have some amount of earth leakage. If all circuits are fed from one RCD then this total leakage figure may be enough to trip the RCD, even though there is no actual fault.
Thanks again, This is just a one bedroom flat, I understood that a single RCD is allowable according to regulations, is that not correct?
Many thanks

Alan
 
Thanks again, This is just a one bedroom flat, I understood that a single RCD is allowable according to regulations, is that not correct?
Many thanks

Alan

How many circuits are there?
Photo of consumer unit would be useful as well if you have one.
 
RCBOs would be an ideal upgrade without excesivs cost. This gives individual RCD protection to each circuit. The main switch would remain as-is.
 
Thats something I had not considered.
So each of the 5 fuses would be replaced by a single width RCBO is that right?
How much would the RCBOs cost?
Would that pass an EICR?
Thanks
Alan
 
You won't get RCBOs for that board. Being cynical here but the amount of undisturbed dust on the conductors and mcb switch toggles did they actually do anything in the consumer unit. If you redact any personal info seeing the EICR could be interesting.
 

Reply to can a consumer unit switch be replaced by an RCD? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, NAPIT report was carried out due to flood, all kitchen appliances, wall/light switches, fire/heaters etc need replacing. The electrician...
Replies
4
Views
927
Hi, Hoping someone can clarify for me. I've recently moved into a rental property, the landlord had new electric radiators installed and a new...
Replies
3
Views
574
Hi All, I am in the middle of purchasing a small 1 bed flat in England, and have been sent a Domestic Electrical Installation Certificate by the...
Replies
1
Views
1K
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
Hi, I am due EICR test on my property which has 20 year old wiring. Last test on 2018 was fine with no issues. Just need to check if my consumer...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock