Alright troops ! First post here ! Any one come over this situation before !
Yesterday i connected an existing feed for cooker good into socket but it wasn’t working when I turned on!
I tested between live and earth (240v) between live and neutral (12v ) and neutral and earth (0 volt )

I suspected the neutral was an open circuit, I rewire a neutral and that worked!

I can’t think why there was 12v between the L and N

thoughts ?
 
Test meter impedance was high enough to see 12V with capacitive leakage !
(That would have disappeared if a little more current was drawn)
( Both terminals at 240V .. No Neutral .. 0 V on meter , Ooops )
 

Reply to Can anyone explain this reading (suspected open circuit) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi folks I've just identified as cause of lighting circuit tripping in consumer unit a low volts ceiling light with laride transformer taking in...
Replies
7
Views
286
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi. I've read much about ac vs dc but can't find a 'simple' answer. If current alternates 50 times per second in a uk mains circuit, why do live...
Replies
23
Views
1K
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
713
A client has a Kenwood CK405 dual fuel range cooker, for which the smaller of the 2 ovens doesn't work. The elements tested out fine, but live...
Replies
5
Views
937

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock