Search for tools and product advice,

Discuss Can anyone tell me what is wrong/incorrect. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
37
0E13BF62-DDB2-4D56-89D8-2755421342E1.jpeg
 
As above plus
grey should be used a N with blue sheath.
armour is not earthed.
 
Perfectly acceptable to use black as the neutral conductor providing it is correctly identified.

The supply is using black as neutral and grey as earth. I would seriously question the competence of someone who cannot even get that correct.
 
Things wrong in this picture;

1. Basic insulation showing (meter cabs are not considered suitable enclosures) interestingly site applied insulation (heat shrink) is no longer classed as suitable in an application like this either.

2. Black being used as the N (personally don’t see a problem with it and I’m not aware of any regs which explicitly state black cannot be used as a neutral) but the NICEIC ran a campaign to “de-neutralise” the black. Bigger problem IMO is no sleeving to identify it as a neutral.

3. Difficult to tell from just a photo but that doesn’t appear to be a 25mm SWA and the cut-out says 100A fuse fitted. So OCPD is too large for cable.

4. Whilst not a 7671 reg most DNOs/DSOs specify that meter tails can only use the cutout fuse as an OCPD where the tails are less than 3 metres.

5. SWA braid is not earthed.

6. SWA is not terminated correctly.
 
Or not as the case might be.

Think there was a debate previously on the forum as to whether a meter box is considered an enclosure because it is lockable (don't laugh) and a key is needed!
According to NICEIC and Select it isn’t classed as a suitable enclosure as non-skilled persons access the enclosure regularly/to read the meter etc.
 
Glanding the cable to a metal fused-switch like the Wylex ones would have been far better, then double insulated tails to the meter.

It looks like the "filler" insulation around the 3 cores has been clamped or similar - wonder how that dent happened?
clamped-bit.jpg
 
Morcombe and Wise, Two Ronnies???

Might I direct you fine gentlemen to another thread….

 
Glanding the cable to a metal fused-switch like the Wylex ones would have been far better, then double insulated tails to the meter.

It looks like the "filler" insulation around the 3 cores has been clamped or similar - wonder how that dent happened?View attachment 112405
Didn’t even see that dent/damage.
Looking at the size of the damage, it could have possibly been some sought of over tightened Earth strap? (But why)? I’ve run out of idea.

Merry Xmas
 
The earth tag does not match the template laid out in BS7671.

The text should read,

"Safety Electrical Connection, Do Not Remove"

Not,

"Safety Electrical Earth, Do Not Remove"

I'd also argue the Hepworth branding should not be there and the standard Earth pictogram is not used.

Pedantic, yes, but it is a noncompliance.
 
mmm! not so sure Id agree it as a non-compliance, Isn't there a passage in the regs that says "alternative 'systems/methods' etc shall not be precluded as long as safety isn't impaired" (or something like that as I Don't have regs book to hand )?

Alternative wording/pictograms hardly impairs safety and message is clear enough!
 
mmm! not so sure Id agree it as a non-compliance, Isn't there a passage in the regs that says "alternative 'systems/methods' etc shall not be precluded as long as safety isn't impaired" (or something like that as I Don't have regs book to hand )?

Alternative wording/pictograms hardly impairs safety and message is clear enough!
OK so I was clutching at straws but it is the kind of thing examiners include solely to stop people getting full marks.
 
I am no expert on the regulations but wondered whether the sixth item is that the main equipotential bonding is done remote from the cutout location.

The according to the book ‘rule abiding‘ installation should have the earth conductor from the incoming N in the cutout going only a short distance to the main earth terminal bar, and then from this bar runs a cpc conductor to the dist boards, and separate EP bonding conductors for say water and gas connected also to the bar as in this figure.

With this scheme the cpc wiring and EP wiring do not share one conductor which might be considered a possible single point of failure. Just musing….

1703601788921.jpeg
 
Last edited:
I am no expert on the regulations but wondered whether the sixth item is that the main equipotential bonding is done remote from the cutout location.

The according to the book ‘rule abiding‘ installation should have the earth conductor from the incoming N in the cutout going only a short distance to the main earth terminal bar, and then from this bar runs a cpc conductor to the dist boards, and separate EP bonding conductors for say water and gas connected also to the bar as in this figure.

With this scheme the cpc wiring and EP wiring do not share one conductor which might be considered a possible single point of failure. Just musing….

View attachment 112486
They replaced meter tails with SWA making the MET remote.
We don't know how the swa terminates or if it is downstream fused.
A bit of a botch, whatever way you look at it.

A Spn fused connection unit would have been the way, but even then could cause a moan from the dno for using the meter cabinet.
 
Last edited:
I am no expert on the regulations but wondered whether the sixth item is that the main equipotential bonding is done remote from the cutout location.

The according to the book ‘rule abiding‘ installation should have the earth conductor from the incoming N in the cutout going only a short distance to the main earth terminal bar, and then from this bar runs a cpc conductor to the dist boards, and separate EP bonding conductors for say water and gas connected also to the bar as in this figure.

With this scheme the cpc wiring and EP wiring do not share one conductor which might be considered a possible single point of failure. Just musing….

View attachment 112486
I'd suggest the opposite.
Suppose you lose the connection between MET and CU ? Your bonding is now probably via the 0.75mm flex to the boiler. By running a connection direct from service head to CU and also taking your bonding cables to the CU, you've eliminated two connections and reduced the risk of incomplete/ineffective bonding.
 

Reply to Can anyone tell me what is wrong/incorrect. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Right or wrong please? , if wrong, what needs to be done to fix it? thanks in advance.
Replies
13
Views
1K
Hello I have some decking lights which to be fair, have been nothing but pain in the bottom since they were installed. Moisture in the lens lamps...
Replies
10
Views
2K
I’m wondering if anyone would be able to tell me if I have a looped supply in my property as I’m looking to install an EV charger.
Replies
4
Views
320
Good morning everyone. I bought some property in northern Michigan and this is on it. Not an electrician, just want to know what it is. I figured...
Replies
2
Views
602
  • Question
Hi folks. Just wondering if anyone can tell me what this is? I was given it a few weeks ago, tried searching the interwebs for info but found...
Replies
4
Views
436

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock