Discuss Can FP 200 be burried in the wall without RCD??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

W

wetny

Hi. We are looking to quote to install domestic heat detectors interconnected to the existing smoke alarms for a social housing provider. Do you think that FP200 could be used to save us installing RCD protection to the circuit as the cable needs to be concealed. Our NIC inspector tells me that t and e can't be used through the ceiling void because you can't guarantee that it's at a depth of 50mm, so FP would seem to be the way forward. I am aware the the cable is fully screened but only by a foil wrap. Cheers.
 
It's not a matter of mechanical protection, more earthed metallic sheath. Without lifting floorboard, carpets and moving furniture, cable can not be clipped. We are talking about 5000 properties, if it was just a few would not be an issue.
 
Last edited by a moderator:
It's not a matter of mechanical protection, more earthed metallic sheath. Without lifting floorboard, carpets and moving furniture, cable can not be clipped. We are talking about 5000 properties, if it was just a few would not be an issue.

But the 'earthed metalic sheath' that they are referring to in the regs, (in order to not need RCD protection), is for mechanical protection.

FP200 sheath does not offer this.

SWA, yes. Steel conduit, yes. Earthed steel plate, yes. But not FP200.:)
 
Last edited by a moderator:
I would have thought that the purpose of earthed metallic sheath was to provide automatic dis connection rather than mechanical protection.
 
It's not a matter of mechanical protection, more earthed metallic sheath. Without lifting floorboard, carpets and moving furniture, cable can not be clipped. We are talking about 5000 properties, if it was just a few would not be an issue.

and how would you earth the foil? sy would be better.
 
I would have thought that the purpose of earthed metallic sheath was to provide automatic dis connection rather than mechanical protection.

You might actually be right with regards to the requirements of that regulation - I've always took it as 'earthed mechanical protection' that was required - I've never thought of it from the point that you're making, but I've just re-read it.:)

So the question, as you were asking, is 'does FP200 fit the bill?
 
Last edited by a moderator:
I had a similar issue with interconnecting alarms and concluded with the use of radio linked alarms. I was initially concerned about compliance, however the manufacturers verified it's compliance with Part B 1.21.

The only issue was location, however positions were acceptable in close proximity to lighting points, and the rigidity of the fp200 enabled a 50mm clearance from point to point.

Mr NIC man and Mr Building Inspector were both happy.
 

Reply to Can FP 200 be burried in the wall without RCD??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I have an Unsatisfactory EICR with the following observations (full report attached, with key details blanked) - the apartment block was built...
Replies
12
Views
6K
Could somebody please clarify a certain aspect of this for me? I have posted in the IET forum and got no reply. So say you install cables in a...
Replies
17
Views
10K
Hi all, as many of us are probably getting lots of EICR's to do on rental properties, I'm just wondering what you guys are coding non RCD...
Replies
26
Views
3K
Hi - sorry, I haven't been on the forum for ages! Its that long I cant see how to attach photos now! I have a couple of queries following some...
Replies
15
Views
3K
The Ghost
T
Eh up :) We all know about the duff max Zs tables in the OSG (Table B6) and GN3 (Table A4)... in fact, I've only just recently updated my GN3...
Replies
11
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock