You rate the cable for the worst installation method with regard to its current carrying capacity, that would be the trunking. Being contained in trunking reduces its current carrying capacity to below that required for a 7.5kw shower.
 
It would also be false economy as you can be certain that someone will want to replace it with a higher rated unit in the future. For the length of run and cost why not use 10mm and perhaps a 9.5kW shower which will perform a lot better in the middle of winter when the incoming water is really cold.
 
Yeah I did think it should be a 6mm minimum but this was wired by somebody else so this cable was already in place, so should i have to say to the customer that the cable needs upgrading,
Thanks
 
The cable is installed in 3 metres of trunking, 3 metres clipped direct, and 5metres in the joist space with no insulation,
Sounds like a fairly easy run to replace the cable.
if you are going to put your name on the certificate, make sure that it is compliment otherwise it will always be a nagging doubt in your mind that some day it will come back and bite you.
 
It would also be false economy as you can be certain that someone will want to replace it with a higher rated unit in the future. For the length of run and cost why not use 10mm and perhaps a 9.5kW shower which will perform a lot better in the middle of winter when the incoming water is really cold.
water is not much colder in winter. 18" down in the ground temp. is fairly constant all year round. at about 10degrees.
 
Yeah I did think it should be a 6mm minimum but this was wired by somebody else so this cable was already in place, so should i have to say to the customer that the cable needs upgrading,
Thanks
I would personally recommend to the customer that the cable requires upgrading as it was incorrectly rated for the installation method in the first place. However, rather than a scaremongering approach, I would focus on the benefits such as the possibility of a larger rated shower unit, like Dave OCD suggested.
 
water is not much colder in winter. 18" down in the ground temp. is fairly constant all year round. at about 10degrees.
If you're using the pumped type the water in the attic is colder in winter

Not sure how common the pumped is the UK ,I think they're mostly mains fed ?
 
New posts

Reply to Can I use a 4mm T&E for a 7.5Kw shower? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
644
Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
418
Hi, I've got a customer who wants a 10.5 kW shower installed in his bathroom. As it happens he already has two unused 4mm T&E cables run from the...
Replies
18
Views
2K
Seen a couple of videos with Doncaster cables now producuing a T&E with the CPC already sleeved so no need to fit our own. I also read somewhere...
Replies
19
Views
865
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
581

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock