I would like to control a Power supply AC/DC connected to mains with an input of 230v (2.4A/115VAC; 1.2A/230VAC) and output 5v / 40A (200Watts). Can I use a switch button rated 3 A @ 250 V AC to turn it on and off? It would be one of these or something similar.
 
I would like to control a Power supply AC/DC connected to mains with an input of 230v (2.4A/115VAC; 1.2A/230VAC) and output 5v / 40A (200Watts). Can I use a switch button rated 3 A @ 250 V AC to turn it on and off? It would be one of these or something similar.

That looks like a momentary switch. You would need a latching one. I haven't checked the voltage/current ratings.
 
you don't want amomentaryswitch you need a single throw on/off switch.
 
as above 40A (200watts) @ 5V is roughly 0.8A @240V. allowing for losses in the PSU , 1A is close to the mark. you'll need some fat cables on the 5V side though. 6.0mm?
 
The PSU is rated at 1.2A, so you need a switch rated for 230VAC or above and current of around 2A or above.
 
Don't forget that SMPSUs can have high inrush that can weld switch contacts together. I would look for a switch with at least 3A inductive or 10A resistive load rating to ensure reliability.
 
That's ok then, the output current may be 40A, but the input current will not be. Remember, power is I x V and so the higher input voltage means less current.
Thank you! Yes indeed I was a bit confused as to which amount of current I was supposed to look at and provide a switch for. First time working with switches and AC.
 
Thank you! Yes indeed I was a bit confused as to which amount of current I was supposed to look at and provide a switch for. First time working with switches and AC.

No problem. Bear in mind Lucien's good advice about choosing a suitable current rating. Your switch will last longer then.
 
Don't forget that SMPSUs can have high inrush that can weld switch contacts together. I would look for a switch with at least 3A inductive or 10A resistive load rating to ensure reliability.
Thank you! This is really useful. The PSU will be powering 11 LED matrices, each potentially drawing up to 3A (though it will stay below that as I won't use full white colours)
 

Reply to Can I use this switch button to turn an AC/DC PSU on and off? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I used 12v dc from a 13 plate car battery to power a 12v dianamo dc motor and brought in an alternator to change the battery using the rotation of...
Replies
7
Views
722
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
359
Hello People Our Enphase solar system needs to have the AC supply shut down via the fire alarm contactors local input output unit that has NO &...
Replies
0
Views
521
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
620
I'd like to find a timer switch, in a style that looks alright next to decora light switches, to control a bathroom fan. The bathroom fan...
Replies
1
Views
943

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock