Discuss Can incoming mains run above ground under suspended floor? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi all. I'm looking for some expert advice on the above. I am having an extension built and the footings are a raft slab which can be built/poured under the existing incoming mains cable (it's in a black pipe approx 50mm dia). There will be a suspended floor approximately 100mm above the slab. Can I leave the existing cable where it is and build the raft below it and floor above it? ie it it allowed to run within the extension but under the floor? I could put a more robust pipe around it for greater protection if necessary? Thanks in advance for your thoughts/advice.
 
Thank you for that, I have sent them an email enquiry as can't get through by phone. It would still be great to get others thoughts on this if they have any, or having any experience of something similar. Thanks again, James.
 
Agree with @Midwest. While the cable may be ok there, you don't want to be working around it while it's live, in my humble opinion. The DNO will give guidance (as it's their cable) and can assist with temporary disconnect while you are working above it.
 
Just had exactly the same.
No you can't build over it as the DNO require access at all times is what I was told.
Having fathered a dno technician I have an unusual relationship with my local dno which did help. We uncovered the dno 50mm duct and put in an external meter cabinet directly over the point where the new wall crossed the supply. The dno disconnected the supply cable from the existing cutout, opened up the duct below the new meter cabinet position and pulled the supply cable back and connected into the new meter position. I then was left with a redundant duct connecting the new and old meter positions down which I fed an SWA which I connected via a switch fuse
 
You should be talking to the supplier AND the BCO.......................

and of course the builder and spark should know this ....
 
Thanks mhar! I feared this might be the case and am obviously worried about the cost implications. Should've fathered a DNO technician ;o). Unfortunately the new house wall above the existing cable (where it crosses) isn't actually a wall, its sliding glass doors so no where to put it - looks like a substantial move of cable and meter might be in order, gulp!
 
Indeed!! A grand and 8 weeks is what someone said. I cried....

The realities of having extensions:

35% of the budget goes under the ground
the other 65% goes very quickly

The 20% contingency fund is spent before you consider internal finishes..........

Best you check that the gas isn't affected too AND based on our experience, make sure you know precisely where all the drains are - we "found" the estate surface water drain where we wanted our foundations to go and a man hole where a wall was due to be built!
 
Hi all. I'm looking for some expert advice on the above. I am having an extension built and the footings are a raft slab which can be built/poured under the existing incoming mains cable (it's in a black pipe approx 50mm dia). There will be a suspended floor approximately 100mm above the slab. Can I leave the existing cable where it is and build the raft below it and floor above it? ie it it allowed to run within the extension but under the floor? I could put a more robust pipe around it for greater protection if necessary? Thanks in advance for your thoughts/advice.
I don’t know if this will work but I did a job in Virginia and they had raised floors about a foot high and installed 35 control cabinets and transformers. We used tray cable wire , did not have to use conduit and that job turned out awesome
 
I don’t know if this will work but I did a job in Virginia and they had raised floors about a foot high and installed 35 control cabinets and transformers. We used tray cable wire , did not have to use conduit and that job turned out awesome
I don't know the OP... but I think it's unlikely he'll want to move to Virginia... but great idea though.
 

Reply to Can incoming mains run above ground under suspended floor? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
890
I have had a kitchen extesion built on an old property (c.1810), which has an unusual consumer unit situation. Part of the property has only a...
Replies
12
Views
2K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
I need to insulate under my suspended floor which has many cables running through the joists (consumer unit is below floor). My main concern is...
Replies
4
Views
5K
Interested in opinions on this. Need to put the boiler (in my own house) in a temporary location for 6 months while an extension is built, when it...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock