Discuss Can Rcd Compensate For High Zs in the UK Electrical Forum area at ElectriciansForums.net

S

spkelectrical

hi currently doing remedial works on a commercial office. I have a lighting circuit on a 6 amp mcb type B within a split load board covered by a 63amp 30ma Rcd . I have taken a zs reading of 750 ohms from a light which is too high . The existing installation is taking its earth from metal conduits embedded in the concrete ceiling.
My question is do I ignore the reading as there is a rcd in place or run a earth wire to the lights. The lights are metal Flaurecents ?
 
The metal conduit should provide earth continuity, at a low resistance, to the lighting circuit, if you are getting a value of 750 ohms then there is a problem with the continuity of the conduit and this should be addressed.

It may be as simple as one loose joint that could be determined from Zs readings along the circuit.
A R2 reading for sections of the metal conduit could also be a useful guide.
Leaving this situation may mean that as the resistance gets higher (if the conduit deteriorates) there could easily be a point where the protection provided by the RCD is no longer effective, so resolution now is the answer.
 
Thank you for the reply. I think the problem is that some idiot in the past has put a plastic board in and forgot to run a earth back to the board that the mcb is in from where ever the conduit enters the cupboard.
 
Connect a temporary lead from the conduit end to the consumer unit earth bar and see if you have an adequate Zs for the circuit breaker, if so then install a permanent earth of suitable csa (probably 4mm² minimum as it is an unprotected cpc) to complete the earthing.
Though if the customer allows it may be wise to check other circuits if they are all earthed via the conduit and are disconnected and consider making up a manifold for all circuits and a single cpc back to the board.
 

Reply to Can Rcd Compensate For High Zs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
493
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
As above the chest level from ground ,metal ANPR housing has no connection to earth ,it has monitors modems and a camera inside with a 230 volt...
Replies
2
Views
668
I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
Replies
44
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock