Discuss Can RCD 'detect' a light fitting short - even if switched off? in the UK Electrical Forum area at ElectriciansForums.net

Darrylle

DIY
Reaction score
1
I have an RCD for the house, and have 3 spotlights to the rear of the house, which I'm in the process of replacing with LED spots.
One wall switch 'feeds' all of them in series. Whilst fitting one of the lights (with only the wall switch off (and taped down!)) - the RCD flipped. I tested this again, and it did the same. There was no current to any of the light fitting wires.
This confused me at first, but then thought: "Hmm can the RCD still sense a 'short' of any of the earth, live or neutral wires?".
Is this possible - even if all wiring is 'correct' and the main light switch is most definitely 'off'?
 
As covered above, in a typical installation the N & E are nominally at the same voltage. In fact, it is that commonality that defines the neutral cable out of the current carrying set.

But cables have resistance & inductance, and currents are flowing elsewhere, so if you measure N - E you will often see a small voltage, usually less than 5V and often just a fraction of a volt. So if there is a N-E short then some of that current flowing elsewhere can find its way round the short and if that reaches the 15-30mA trip threshold for the RCD, it fires.

N-E shorts are often a problem as, for example, you find the RCD trips when someone uses the shower. You assume it is the shower's circuit that is at fault (which for a L-E leak it would be) but in reality the fault could be N-E on another circuit and it is only when enough current flows that it trips.

Many an electrician and DIY'er has wasted hours trying to pin down the fault if they don't know to start off insulating testing N as well as L to rule this out!
 

Reply to Can RCD 'detect' a light fitting short - even if switched off? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. Removed an ancient light fitting, replaced with a newer one, the light comes on but can't be turned off with the switch. It was working...
Replies
23
Views
830
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
881
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi Family member has moved into this house which is about 110 years old. Bodges everywhere inc the electrics. We are just rennovating it and when...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock