Discuss Can someone explain how these storage heaters were wired via the contactor? in the UK Electrical Forum area at ElectriciansForums.net

There are only 4 poles in the contactor, with one pole for each circuit. There are 7 off peak circuits (that I can see). Hence the 3 individual relays, one each for the other 3 circuits. There were probably originally 7 of the relays, or 2 of the 4 pole contactors.
You can think of a contactor as a relay with the ability to switch higher current loads.
 
but I still don’t understand the role of the relays in this configuration- Why are they there when it could just be the contactor, with the load of the contactor supplying the power to the MCB’s during E7 hours?
As shown in the Electratec link Oscar21 posted (#21) they were originally all single relays across the top, total number would depend on how many heaters installed, 1 for each heater, 1 for the Top immersion heater and 1 for the bottom immersion heater.
The relays are used as the Electec controller cannot switch the heater loads, it just uses a control signal for the relays.

Sometime in the past some relays have failed and have been replaced by a 4 pole contactor, (effectively 4 relays in one) probably cheaper or happened to be in the van.
 
What usually happens is either the control panel or the brainbox goes kaput, you cant get the spares for them so they need adapting. As you can see the 3 original relays that are left are 2 x immersion ones and one bedroom heater, these will no longer be in use and I think the OP said the immersions are just on a switch now so the relays will have been bypassed, he also said one of the bedroom heaters was now a panel heater so that relay will have been bypassed as well. In fact you can see there aren't any 24V contol inputs to the A1&A2 contacts on the relays anymore.

Whats left is 4 storage heaters (if all 4 ways are in use) but these still need some kind of control so 4 of the relays have been removed and replaced with a 4 pole contactor controlled by a time-clock elsewhere or even the meter itself.

Edit : its 3 storage heaters still in use, you can tell by the labeling.
 
Last edited:
Thought this was sounding a bit familiar.
A thread on the same subject from 2021,,
There's a link to the manual, but no diagrams, in my post #2

 

Reply to Can someone explain how these storage heaters were wired via the contactor? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
789
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
912
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
202
I get asked quite a lot about replacing old storage heaters with something more economical and I don't know what to recommend. Some people ask for...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock