Discuss cannot find incoming water question in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
37
Hello, yesterday I went to look at a small job, just an extra socket for a garage door. Bonding to gas is visible, where its fed from the CU in 10mm, but nothing to water. Long story short we couldnt find the incoming water anywhere despite looking in all usual places like under sink, under all the kitchen cupboards, under stairs, in the garage ect ect. Could not find anything atall even resembling incoming water so told the customer I need to test with meter (boiler disconnected) to verify its earthed ect. Thing is it might be plastic incoming, probably not, but might be. What would you do in situations like this ? Just interested. No response to my quote btw, customer probaly thinks im pulling her leg !
 
The danger here is probably mostly when on TN-C-S as if water is extraneous and not bonded, you might well find all of the neutral current in an open-PEN fault exiting via the CPC to a shower unit or (not so likely here) the power cable CPC to a gas boiler, neither of which could carry tens of amps for however long it takes the DNO to fix something.

Bonding gas and all water pipes at the boiler, and hot-cold tap feeds at any sinks, would achieve it provided the plumbing is not plastic in places. Which of course is not likely to stay that way after any repair work these days...

You might want to check with any neighbours to see if they know where their supply pipe is and the house/flat shares a similar design and construction?
 
The danger here is probably mostly when on TN-C-S as if water is extraneous and not bonded, you might well find all of the neutral current in an open-PEN fault exiting via the CPC to a shower unit or (not so likely here) the power cable CPC to a gas boiler, neither of which could carry tens of amps for however long it takes the DNO to fix something.

Bonding gas and all water pipes at the boiler, and hot-cold tap feeds at any sinks, would achieve it provided the plumbing is not plastic in places. Which of course is not likely to stay that way after any repair work these days...

You might want to check with any neighbours to see if they know where their supply pipe is and the house/flat shares a similar design and construction?
Not so much a danger on a TN-S, which it is. I could ram in a temp earth rod and IR test between that and a water pipe(s) in the house. Then if the water is extraneous like you say bond to boiler and check for plastic sections. She wont go for that thou. It does annoy me when this happens, builders have previously "revamped" the place and likely boarded over the water mains. That said ive seen some houses where main stopcock is outside in the pavement but at least the pipe is visible where it comes in !
 

Reply to cannot find incoming water question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
464
I recently did a load of work making good a poor installation for a friend who just bought a flat. I have some electrical qualifications and 30...
Replies
10
Views
2K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
So I have been asked to look at a job which includes providing 2 submains (one for a small dwelling, the other for a small workshop/garage). The...
Replies
9
Views
4K
Hi all, it's been a while but been busy in work and setting up my fledgling company I have a question, have a eicr tomorrow on a ground floor ex...
Replies
41
Views
13K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock