Discuss Cannot get RCD test to work? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,604
Evening chaps..

I have just fitted some downlights in a bathroom and needed to give them RCD protection as there was none. I fitted the following:

rcd unit.jpg

The test button works fine and the unit trips when a fault occurs (touching neutral to earth) but I cannot get the MFT to test it for trip times which I need for the MWC. Its a fairy decent MFT and I've never had any trouble with it testing RCD's before but I have never tested this sort of RCD before, it has always been in the CU. I make contact with the live/neutral/earth of something which the RCD is feeding, I get the little 'tick' on the MFT and then it just wont test.

Am I missing something simple here? Is this unit tested in the same way as you would an RCD in a CU?
 
In addition to Howards post above ^^^^ Have you tested the ELI prior to fitting the RCD ?, because if the earth loop is high resistance/non-existent, the tester will inhibit the test if the CPC rises above a pre-set touch voltage, usually set @ 50V, some testers allow this to be set @ 25V, so check this too.
 
In addition to Howards post above ^^^^ Have you tested the ELI prior to fitting the RCD ?, because if the earth loop is high resistance/non-existent, the tester will inhibit the test if the CPC rises above a pre-set touch voltage, usually set @ 50V, some testers allow this to be set @ 25V, so check this too.

I forgot that bit, thanks. prior to carrying out a RCD test, the earth fault loop impedance value must be confirmed as compliant. That is an answer in the 2394/5 exam as well.

Cheers............Howard
 
Evening chaps..

I have just fitted some downlights in a bathroom and needed to give them RCD protection as there was none. I fitted the following:

View attachment 23855

The test button works fine and the unit trips when a fault occurs (touching neutral to earth) but I cannot get the MFT to test it for trip times which I need for the MWC. Its a fairy decent MFT and I've never had any trouble with it testing RCD's before but I have never tested this sort of RCD before, it has always been in the CU. I make contact with the live/neutral/earth of something which the RCD is feeding, I get the little 'tick' on the MFT and then it just wont test.

Am I missing something simple here? Is this unit tested in the same way as you would an RCD in a CU?
Yes, test the same way, it is just and RCD incorporated into a Switched Fused Spur. Double check polarity and ZS on load side of unit. Also prove your meter on another RCD. You may have a faulty unit.
 
Did you test on the outgoing terminals or at the end of the circuit?

The RCD feeds a junction box which feeds the lights and also a fan in the bathroom. I tested at the triple pole switch which I fitted. I tested on the coductors coming from the junction box and the MFT gave a tick 'measurement can be performed'.
 
In addition to Howards post above ^^^^ Have you tested the ELI prior to fitting the RCD ?, because if the earth loop is high resistance/non-existent, the tester will inhibit the test if the CPC rises above a pre-set touch voltage, usually set @ 50V, some testers allow this to be set @ 25V, so check this too.

Zs was 0.9, I'll have a look at the pre-set touch voltage.. Thanks Spark68
 
Yes, test the same way, it is just and RCD incorporated into a Switched Fused Spur. Double check polarity and ZS on load side of unit. Also prove your meter on another RCD. You may have a faulty unit.

Have triple checked polarity (as I was tired!), Zs is ok and I proved the meter on another RCD in the same house.
 
New posts

Reply to Cannot get RCD test to work? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
320
So, I was messing around yesterday with some old testers I have laying around to see if they still work I found my dads old Robin MFT and noticed...
Replies
8
Views
526
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
569
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
236

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock