Discuss Car Charging Point Domestic in the UK Electrical Forum area at ElectriciansForums.net

Lads

Be asked to provide a dedicated 32A supply for a future charging point. Does the circuit need a 32A Type A RCBO

Chris

Should be type A but depending on what charge point you are using it could have a type A RCD built in to the charge point.
If you are not sure what charge point you are using I would install the cable in a method/cable choice that doesn't require RCD protection as obviously you wouldn't want to end up with two 30ma RCD's in series.
 
AMD 2 requirements for RCD protection of a car charging point (not the supplying circuit (necessarily))
AMD2 RCD requirements.jpg
 
Last edited:
Cheers

but the customer does not know yet as it is only for future install, he has said the charging point will come with the car, also current CU is full with no spare ways. So was thinking of installing a small 50A Mini CU at incoming with RCD. Run armoured to garage to a Garage CCU as he wants a couple of sockets and lights and power for electric door. Is this ok
 
Cheers

but the customer does not know yet as it is only for future install, he has said the charging point will come with the car, also current CU is full with no spare ways. So was thinking of installing a small 50A Mini CU at incoming with RCD. Run armoured to garage to a Garage CCU as he wants a couple of sockets and lights and power for electric door. Is this ok

If you are installing the cable using SWA then It doesn't require RCD protection between proposed new ccu at the mains position and garage.
 
Why put the RCD at the supply end and then run it in SWA?
Unless you have a TT system, run a fused supply in SWA to the garage and then RCBO for the sockets and an RCBO for the lights, if required.
If the supplied charger does not have RCD protection when it arrives then fit a type A RCD for the charger.
 
You could install a sŵitch fuse at mains, swa to garage, main switch ccu in garage, RCBO for sockets, RCBO for lights if required wire charging point in swa/ installation method that doesn't require RCD protection so can be put on an mcb incase charging point has built in RCD, if it hasn't then you could swap mcb for charging point for a type A RCBO.


Edit: took me ages to type as have had a few bevvies and Richard beat me to it.
 
Last edited:

Reply to Car Charging Point Domestic in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Would any fellow electricians consider using an open PEN device to protect a metal trailer used as a "Canteen". It is likely to be often connected...
Replies
3
Views
287
Hi What the Maximum number of EV charge points that you can install in a Domestic system.
Replies
2
Views
235
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
582

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock