Discuss caravan park distribution setup in the UK Electrical Forum area at ElectriciansForums.net

C

chrisfs150

I've been asked to wire a caravan park up so far the system consists of:
connection boxes with each socket on a 16 a trip 30mA rcd
SWA to each conn box buried to 600mm+
Incoming supply is t.n.s
But....The main distribution board is 3phase so do I have to have the distribution cct on mcbs alone (1 for each dist cct)
Or doe each cct need to be on a 100ma rcd? If so that ain't going to fit my 3 phase board so do i now need to come from my 3phase MCBs out to a separate board holding my 100ma RCDs then out to my ditribution ccts? Or is it possible to get 60/80a rcbos that will fit?
 
you don't need to protect SWA with a RCD. main concern is what sizw SWA? ccc? Volt drop calculations?
 
what do you expect on a friday night with the beer going down faster than the titanic.
 
I've been asked to wire a caravan park up so far the system consists of:
connection boxes with each socket on a 16 a trip 30mA rcd
SWA to each conn box buried to 600mm+
Incoming supply is t.n.s
But....The main distribution board is 3phase so do I have to have the distribution cct on mcbs alone (1 for each dist cct)
Or doe each cct need to be on a 100ma rcd? If so that ain't going to fit my 3 phase board so do i now need to come from my 3phase MCBs out to a separate board holding my 100ma RCDs then out to my ditribution ccts? Or is it possible to get 60/80a rcbos that will fit?

I think you should get an electrician experienced in this field in to have a look at the work fella. It would appear that it's been a while since you picked up a regs book and could potentially learn a lot from someone who has done this type of work before.

This isn't a dig at all, but the question alone leads me to think that you're slightly out of your depth. If this were a Electrical Trainee posting this question, they'd be getting hammered right about now!
 
everybody specialises in a couple area's for example with is we do a lot of bms, controls etc.

have never set up a plc etc so if I ever needed to I would call in a favour from a guy ive done some work for in the past.
 

Reply to caravan park distribution setup in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

After my last post and having and having to re-learn some stuff can someone check and advise on a few things. Sorry if this is wrong don't hate...
Replies
7
Views
2K
Hi guys, New job looking at. I havenā€™t been to site yet, but this is the scenario. DNO just put a new single phase supply into a field PME...
Replies
5
Views
1K
Hi everyone, I have a quick question if I may? I'm thinking of adding a second PV system to my existing rooftop PV & battery setup. As the...
Replies
0
Views
1K
I am pricing a job to wire 21 new pitches for a caravan park. There will be a meter box beside each caravan with a 16a trip. I will split it into...
Replies
4
Views
3K
hi all i was just in the middle of doing an eicr on a caravan park and wanted some opinions on what codes are relevant to the site. ive got tncs...
Replies
32
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock