Discuss Caravan suppły RCBO in the UK Electrical Forum area at ElectriciansForums.net

Bsharp

-
Reaction score
22
Hi I haven't posted for a while but I'm having some issues with a caravan park I have recently carried out some work on and washoping somebody may be able to shed some light on the issue.
The problem is burnt out neutrals on out going side of RCBO, we have replaced 137 caravan suppły points I've the winter and now the camp is back open the problems have started, I have replaced 5 RCBO'S up to now all with the same BADLY burnt out neutral, now I know the obvious answer is loose connection on the neutral but was wondering if any body had come across the same problem with a different cause as we check all manufacturers connections. The supplies have been reduced to only 10amps!! (By instruction of camp owner to reduce electricity consumption as the camp pays for the electricity)
i can't see any overload issues apart from the standard "nuisance tripping" until caravan owners decrease the power they are using. The reason may just be the odd loose neutral but in my 25 years of work I have never seen so many in such a short space of time! Any ideas would be great fully recieved.

Thanks.
 
Have you checked the resistance acroos the incoming and outgoing neutral connections to make sure it is not a hight resistance joint?
 
Quite possibly I'll be carrying out a few resistance test tomorrow on a few random rcds around the site. I'm starting to think this could be a problem with the manufacturer
 
If you put a load on the circuit and measure the voltage each side of the RCBO you will able to see what it's resistance is under load.
 
Last edited:
Do you think that the fact that no boot lace ferrules have been used in the boxes by the manufacturer that the fine cores of the fly leads which appear to be spread could cause a high resistance joint??
 
Do you think that the fact that no boot lace ferrules have been used in the boxes by the manufacturer that the fine cores of the fly leads which appear to be spread could cause a high resistance joint??

It wouldn't necessarily cause an increase in resistance, but it can create a significant reduction in CSA at the point of the connection. But it depends on the type and design of the terminal. A cage type terminal such as you get in MCBs and din rail connectors where a flat plate traps the conductor against another plate is unlikely to suffer as much as a standard screw terminal.
 
The terminals are din rail connectors direct into RCBO, no screw terminals are used like we see in neutral bars, surely the decreased csa of the conductor could cause a high resistance taking into account these vans are only on 10amp supplies so are pulling very close to the maximum??
 

Reply to Caravan suppły RCBO in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
897
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
Hi, I have been having issues with our fridge causing my modem and video card on my pc to drop out. -They are on the same ring circuit, have...
Replies
8
Views
796
Good afternoon all, I have been asked to look at a problem with a bolted neutral but no one seems to know what exactly is the problem. SSE...
Replies
0
Views
689
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
332

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock