Discuss Category for lack of RCD on sockets in 27 year old building in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
6
There is a difference of opinion in that a testing company carrying out an EICR has classed lack of RCD protection as a C2 where I understand this type of fault to be a C3 according to Guidance Notes 3 Table 3.5. Their opinion has been formed in reference to a publication called EICR Code Breakers as per the attachment. I had not heard of this book previously and have ordered a copy to see if there is something there I am unaware of but whilst I wait for delivery I thought I would throw it out there to see if anyone else has experience of this?

The building was erected early to mid nineties I would guess it came under 16th edition amendment 2. I am pretty sure it is mostly in galvanised and earthed conduit though I don't know every inch and therefore the reference to PVC/PVC may be correct in some instances. As far as I can see there are no high readings in the test certs that would mean the MCB protection is compromised.

Your thoughts appreciated
 
TL;DR
Category for lack of RCD on sockets in 27 year old building

Attachments

  • General Socket Protection.pdf
    1.2 MB · Views: 17
sockets that may be used outside is a C2. general sockets can be either C2 or C3, down to the inspector's judgement.
 
sockets that may be used outside is a C2. general sockets can be either C2 or C3, down to the inspector's judgement.
Thanks Telectrix. I will have to visit site and find the locations. It is a three storey office block so it would be unreasonable to assume anything above ground floor could be used for externals. I note your comment that it is up to the tester whether to record a C2 or C3.
 
Why not just fit an RCD socket. Would of been quicker than posting on here.
In the first instance it is a query about whether I am wrong to assume this is a cat 3 but to answer your question, it is a 3 storey office block and the fault is recorded on nearly all circuits serving socket outlets, the estimate to correct the C2 is into the thousands.
 
Why not just fit an RCD socket. Would of been quicker than posting on here.
I should also have mentioned that a very real concern is that the circuits were not designed for RCDs at source so the office equipment is likely to cause nuisance tripping due to computers etc as circuits cover several offices. We may be talking additional circuits which could mean bigger DBs.
 
I should also have mentioned that a very real concern is that the circuits were not designed for RCDs at source so the office equipment is likely to cause nuisance tripping due to computers etc as circuits cover several offices. We may be talking additional circuits which could mean bigger DBs.
This was my reason for asking what type of building it was

Back then CRT computer monitors were the norm and they had a known leakage current which would limit the number of computers you could have on an RCD protected circuit in some cases the RCD's were omitted for that reason
With the move to LCD type monitors the high leakage currents have been eliminated
 
This was my reason for asking what type of building it was

Back then CRT computer monitors were the norm and they had a known leakage current which would limit the number of computers you could have on an RCD protected circuit in some cases the RCD's were omitted for that reason
With the move to LCD type monitors the high leakage currents have been eliminated
Thank You UNG that is something I did not know. Very much appreciated.
 

Reply to Category for lack of RCD on sockets in 27 year old building in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Wouldn't normally note this as an observation on a report but feel I need to. The way the building has been wired is all circuits on L1 have been...
Replies
6
Views
1K
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
2K
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
866
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
764

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock