Discuss Certificate for additional certificate in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Numb

-
Reaction score
0
say I installed a new cooker cercuit to an existing installation and the customer wants a certificate for the work done do i need to test all the other circuits and record all results for the full instal or just test the circuit I installed and record that also if ther is no main bonding to gas + water do they have to get this installed before certificate can be issued or can I just do a cirtificate for the circuit I installed ? by the way this is a made up Sanorio I’m studying 2391 at college just getting my head around certification
 
You would do an EIC as it is a new circuit. You would just put the circuit that you have installed on it.
If main protective bonding was required, You would need to ensure it was satisfactory.
 
So in this circumstance the customer refuses to pay for bonding to be installed what would be the correct action to take, leeve the new circuit you installed isolated or is it down to the installer to make sure main bonding is in place when installing the cooker circuit?
 
So in this circumstance the customer refuses to pay for bonding to be installed what would be the correct action to take, leeve the new circuit you installed isolated or is it down to the installer to make sure main bonding is in place when installing the cooker circuit?
if customer refuses to pay for earthing/bonding to be installed,then you'd advise that you can't carry out the work. end of.
 
No was goin thru certification an they say if your adding a new cercuit to an existing installation you have to do initial verification but I don’t get if I went to an house say they wanted a new cooker point puttin in so you install the new cercuit then test your work but the EIC requires satafactory bonding but you find the install as no bonding who’s that down to to cuz you have already give a quote for the cooker then you turn around an tell them it’s going to be X amount to install bonding before I can energise the circuit they will be like on ya bike so my question is what do ya do ere lol
 
Just thinking on this . I suppose you could check if the new Cooker can simultaneously be touched together with any extraneous parts. If it is not then technically you have not made the installation any less safe by adding the cooker circuit and bonding is not relevant to the part you have installed. You would need to write that on EIC though and tick N/A for bonding.

Just seen it says you're from Manchester. ...the respectable thing to do would be to take the cash and not issue a cert surely lol ;)
 
Before you install ANY circuit to an existing installation, you would check for bonding etc during your initial visit, before you quote for the job or if you quote without doing an initial verification (very unwise), you would check for bonding before you even think about installing the first part of cable.
 

Reply to Certificate for additional certificate in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Not sure whether this is the right context or even forum to mention this, but I’ve recently been offering out myself to a friend to help get his...
Replies
7
Views
399
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
881
Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
699
Hi all, I’m currently doing an electrical installation & maintenance apprenticeship (EAL) and wanted to know what additional qualifications you...
Replies
2
Views
473
Hi Everyone, I had a new consumer unit installed in December 2021, the electrician said that he had more testing to complete and would come back...
Replies
28
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock