Discuss Certification Questions in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
I have just replaced an old style wired fuse board with a modern consumer unit.

When removing the old unit, the 32 AMP wire fuse that supplied two 2.5mm cables to the dining room and lounge sockets I assumed to be a ring main but found no continuity between any of the wires and on further investigation found that it was in fact two radial circuits connected to the single fuse (naughty!)

I don’t want to have to re-wire to install a ring main, so is it within regulation to separate these two radials and supply them from a 20A RCD? Certainly looks safe on paper as 2.5mm is rated at I believe 27amps?

Another frustration is that the layout of the two radials is not consistent, one feeds the dining room and part of the lounge, the other feeds only two sockets in the lounge. I was thinking these should be labelled as “Lounge and Dining Room Sockets (partial)” in the consumer unit. Again, is this allowed?

There is a ring main that supplies the upstairs and the kitchen – odd considering the radial design downstairs – which some bright spark has taken a 2.5” spur off the back of one of the kitchen sockets to supply the downstairs toilet light. Again – how does this stand from a regulatory point of view. I don’t see a safety issue as long as this is labelled up in the consumer unit.

Also in the kitchen, the original 45 amp cooker wire has been fed into a 13A fused spur and the under cupboard kitchen lights & a double 13A socket (ran with 1.5mm twin and earth) has been fed. When I installed the consumer unit it made sense to radial this off the kitchen/upstairs ring main at the unit itself. Doesn’t look regs, but don’t see any danger here as the 13A fuse in the spur would protect from overload of either the sockets or lighting.

I plan to get the installation inspected and signed off. Would all/any of this pass, or is remedial work needed?

Many thanks
 
I have just replaced an old style wired fuse board with a modern consumer unit.

I plan to get the installation inspected and signed off. Would all/any of this pass, or is remedial work needed?

Many thanks

Is this your house?

What made you think doing it yourself was a good idea? ..... not many sparks will sign off AND notify under part P, work they haven't done ..................
 
Unless it is a full re-wire or you dig out and inspect every inch of cable, all electricians are to some extent signing off someone else's work? Does no electrician ever sign off unless they have installed every piece of cable from the meter box onward?
 
If I were to "third party" sign off work I would normally only do so if first the design for the circuits were inspected by me. Then I would need to see the install as it progresses with testing at appropriate stages. I would say that circuits that you are describing are messy and not within the "deemed to satisfy" as conventional Ring Final Circuits. Therefore I would not sign off such work. I would need to be satisfied as to the competency of the person doing the work, which from what you describe would not meet the level of competency required. This is not just me talking. The scheme I am with does allow third party signing which is very specific as to what it will endorse and the conditions I must meet to be supported by the scheme to third party sign.
I would say you might be better employing an electrician to make the radials you descibe into a ring for one thing. I am not trying to rain on your parade just trying to inform you on a legal/regs level what is required.
When you say you don't see a safety issue, the only way you can qualify that is with a full set of tests as required in BS7671. I can assure you that gaining that knowledge requires quite a bit of study, money and experience.
 
Unless it is a full re-wire or you dig out and inspect every inch of cable, all electricians are to some extent signing off someone else's work? Does no electrician ever sign off unless they have installed every piece of cable from the meter box onward?

You clearly don't understand the requirements, scope of work, etc.

So if your house burns down in a months time and the fire brigade states the source is the fuse board, and your insurance refuses to pay up, can you afford to cover the losses?
 
I plan to get the installation inspected and signed off. Would all/any of this pass, or is remedial work needed?
there two hopes
upload_2017-10-7_11-9-50.png
bob hope and no hope!
 
You have a point on this to be fair.

In order to sign this off I would do the test and inspection, Undo all your work and then re do it myself. Not a mammoth task on a CU change if I'm honest.

The bulk of the work on a CU change is normally the test and inspection.
 
I have just replaced an old style wired fuse board with a modern consumer unit.

When removing the old unit, the 32 AMP wire fuse that supplied two 2.5mm cables to the dining room and lounge sockets I assumed to be a ring main but found no continuity between any of the wires and on further investigation found that it was in fact two radial circuits connected to the single fuse (naughty!)

I don’t want to have to re-wire to install a ring main, so is it within regulation to separate these two radials and supply them from a 20A RCD? Certainly looks safe on paper as 2.5mm is rated at I believe 27amps?

Another frustration is that the layout of the two radials is not consistent, one feeds the dining room and part of the lounge, the other feeds only two sockets in the lounge. I was thinking these should be labelled as “Lounge and Dining Room Sockets (partial)” in the consumer unit. Again, is this allowed?

There is a ring main that supplies the upstairs and the kitchen – odd considering the radial design downstairs – which some bright spark has taken a 2.5” spur off the back of one of the kitchen sockets to supply the downstairs toilet light. Again – how does this stand from a regulatory point of view. I don’t see a safety issue as long as this is labelled up in the consumer unit.

Also in the kitchen, the original 45 amp cooker wire has been fed into a 13A fused spur and the under cupboard kitchen lights & a double 13A socket (ran with 1.5mm twin and earth) has been fed. When I installed the consumer unit it made sense to radial this off the kitchen/upstairs ring main at the unit itself. Doesn’t look regs, but don’t see any danger here as the 13A fuse in the spur would protect from overload of either the sockets or lighting.

I plan to get the installation inspected and signed off. Would all/any of this pass, or is remedial work needed?

Many thanks

You have no chance of getting it signed off. You should pay a sparks to do an eicr, then pay him to fix all the departures, he will then give you a satisfactory eicr. It’s about the best you can hope for.
 
I was told by a insurance lose adjuster once. some body did that to their house and it burned down
where is the test certs for this. try to blame a sparky said that he had fitted it .
he came clean .sorry we will not pay you for the house has burned down.
 
Thanks Bill.
So actually I am no worse off than I was before.
I am 100% safer than when I had the wired unit in place & less likely to have the fire brigade rescuing me from a bedroom window. Can anyone say sensibly why the new installation would be *more* dangerous than the old one?
I haven't made any changes to any of the wiring in the house outside the old unit (the wiring in the kitchen was in place when I bought the house) so at worse I would have to get a spark to put a new unit in place some time in the future.
 
Thanks Bill.
So actually I am no worse off than I was before.
I am 100% safer than when I had the wired unit in place & less likely to have the fire brigade rescuing me from a bedroom window. Can anyone say sensibly why the new installation would be *more* dangerous than the old one?
I haven't made any changes to any of the wiring in the house outside the old unit (the wiring in the kitchen was in place when I bought the house) so at worse I would have to get a spark to put a new unit in place some time in the future
part p numskull .and your insurance and your solicitor who sells you house.
 
I am 100% safer than when
That statement in relation to what is stated above is totally incongruent to put it politely. You are aware that what you have undertaken is notifiable work yes? You are required by law to notify BC a minimum of 48 hours before work commences. If you do not you are commiting an offence. Aside from that you are aware of the impact on sale of a property in such circumstances not to mention the insurance implications?
As to the question of safer, can you put up on here a full set of tests results and schedule of circuits that show that the work you have done is safer?
 
Last edited by a moderator:
Thanks Bill.
So actually I am no worse off than I was before.
I am 100% safer than when I had the wired unit in place & less likely to have the fire brigade rescuing me from a bedroom window. Can anyone say sensibly why the new installation would be *more* dangerous than the old one?
I haven't made any changes to any of the wiring in the house outside the old unit (the wiring in the kitchen was in place when I bought the house) so at worse I would have to get a spark to put a new unit in place some time in the future.
I think you misunderstood my point mate, you have carried out a major piece of electrical work, something you are not qualified to do. you should get a qualified sparks to look at it in conjunction with a full test. Then get him to rectify any faults he finds. Weather your dabbling has made your house safer is impossible to say. Get a test done quickly.
 
The danger comes from inadvertent poor workmanship and not rectifying existing faults.

Poor connections cause fires.

You may think all is well and it may well look ok but one slip up can have catastrophic consequences.

Part of a board change is testing and inspecting the existing installation as over time the installation is degraded.

Most of the time if a board change is required there are other faults to rectify which will not get better over time.

The reason we all now have to fit metal consumer units in domestic premises is the likelihood of a fire starting in one caused by poor workmanship or materials.
 
That statement in relation to what is stated above is totally incongruent to put it politely. You are aware that what you have undertaken is notifiable work yes? You are required by law to notify BC a minimum of 48 hours before work commences. If you do not you are commiting an offence.
So is having a smoke in your van if other workmates travel in it, but never seen anyone prostituted prosecuted for it. it's also an offence to light up in the vehicle if little monsters kids are being transported. also. from the 1872 licencing act, it is illegal to be drunk in a pub. severe penalties may be incurred, e.g. transportation to Australia. think i might go for that one. 10 pints is a hell of a sight cheaper than Ryanair.
 
Paul have you tested the circuits you've connected to your new CU so that you'll sure they were safe to energise?

Without Sorry for boring the pants of other members, pictured below is a socket I discovered when a new kitchen had been installed in a house. It was a socket on a ring final, that had been plastered over when the house was built circa 1960, the ring was changed to two radials in 2011 when someone replaced the CU. The cables were still live, until hacked out the plaster to reveal this old fossil, and disconnected from the radials.

Socket1.jpg Socket2.jpg
 
Don't misunderstand the nature of what is being purported to you. This is meant in the spirit of guiding you safely through such a project. It would have been better to post here at the planning stage. I am all for you doing such a project and applaud your sense of adventure and derring do, but of course we are constrained by regs/statute and can only advise accordingly.
 
Paul have you tested the circuits you've connected to your new CU so that you'll sure they were safe to energise?

Without boring the pants of other members, pictured below is a socket I discovered when a new kitchen had been installed in a house. It was a socket on a ring final, that had been plastered over when the house was built circa 1960, the ring was changed to two radials in 2011 when someone replaced the CU. The cables were still live, until hacked out the plaster to reveal this old fossil, and disconnected from the radials.

View attachment 38701 View attachment 38702
just bang a couple of wagos on it.

showing----.gif
 
having a smoke in your van
It is a matter of scales of danger really, someone phoned me from the number on my van and told me I am smoking in the van. I didn't get prosecuted though, should have been though;) I did tell them I would discuss this with the heinous offender when he got back to the office.
 
Edit In reply to Mr Moonie.

It was simpler just to disconnect t'other ends and as the back box was going to be behind a floor unit, safer for the Sunday afternoon diy'er and power drill ;)
 
Have you checked the incoming meter tails and bonding ?. As the work you have done is change the consumer unit all work by you can be inspected i.e. not concealed in the fabric of the building and I can't see a problem with a third party signing that part of the work off if complies ,however I agree what Vort has posted the correct procedure has not been followed and this ( in part) is down to public awareness. As this is not my line of work I assume that members on here who do consumer unit updates would include a full EICR on the existing installation prior to re-energising it and I encourage you to do this.Midwest in post 19 has proved a very good example in his post may be this is something you should be investigating.
 
It is a matter of scales of danger really, someone phoned me from the number on my van and told me I am smoking in the van. I didn't get prosecuted though, should have been though;)
haha. reminds me of t'other week. stopped at traffic lights, 2 lanes. car next to me in other lane. i chucked my smoke end out and he went ballistic. yelling and bawling " cigarette end.litter... blah, blah, blah. "

so i wound down my manual window winder and yelled back at the pratt.....

" if you're quick, there's still a couple of drags left on it "

don't think he was amused.
 
haha. reminds me of t'other week. stopped at traffic lights, 2 lanes. car next to me in other lane. i chucked my smoke end out and he went ballistic. yelling and bawling " cigarette end.litter... blah, blah, blah. "

so i wound down my manual window winder and yelled back at the pratt.....

" if you're quick, there's still a couple of drags left on it "

don't think he was amused.

Advise against chucking things out of windows or this could happen :D

WATCH: Driver throws rubbish onto the street but suffers instant karma when THIS happens - http://www.express.co.uk/life-style/life/838397/Upload the image directly to the thread-viral-video-karma-driver-litter

Edit after the F in adverts!
 
Paul have you tested the circuits you've connected to your new CU so that you'll sure they were safe to energise?

Without Sorry for boring the pants of other members, pictured below is a socket I discovered when a new kitchen had been installed in a house. It was a socket on a ring final, that had been plastered over when the house was built circa 1960, the ring was changed to two radials in 2011 when someone replaced the CU. The cables were still live, until hacked out the plaster to reveal this old fossil, and disconnected from the radials.

View attachment 38701 View attachment 38702

All very well, but in truth lets assume during a board change we discover the ring is actually not a ring, and IR tests are good....then how many of us would have discovered that hidden horror? Particularly if it's an old installation where wiring is not always text book. Suspicions might be aroused if the rest of the wiring was text book and it was clear the kitchen had been altered, and you'd expect those ends to drop the IR through the floor.
Otherwise, without any obvious problems I doubt very much I would of found it during a board change. I'd have made it two radials.
 

Reply to Certification Questions in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
767
I found a 13A FCU, connected to the kitchen ring supplying an outdoor junction box, providing two SWA 2.5mm radials. Unconventional? yes. One...
Replies
2
Views
872
All sockets wired radial, 2.5mm, lighting 1.5mm. Question 1. Is it ok to have two radials on one CB? No more than 4 outlets on each radial...
Replies
1
Views
624
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
678
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
769

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock