Discuss Changes in the 17th edition.... in the Australia area at ElectriciansForums.net

Reaction score
24
Thought I'd start a sticky post on the 17th edition changes, basically just list of all the regs which have changed, be as detailed as you like really, hopefully it'll become a decent reference post for you look upon in the furture months before it comes into action. Type away...........
 
i'm gonna start writing my 17th edition and 17th edition update courses next week, so my head will be well and truly in the book

I can always post the main points up here, no probs
 
reg no. 411.3.3

In a.c. systems,additional protection by means of an rcd in accordance with regulation 415.1 shall be provided for:

(i) socket outlets with a rated current not exceeding 20A that are for use by ordinary persons and are intended for general use,and

(ii) mobile equipment with a rated current rating not exceeding 32A for use outdoors.

An exception to (i) is permitted for:

(a) socket outlets for use under supervision of a skilled or instructed persons, e.g. in some commercial or industrial locations, or

(b) a specific labelled or otherwise suitably identified socket-outlet provided for connection of a particular item of equipment.


not sure if i am interpriting the (i) correctly? any thoughts?
 
leeroy,

it is what it is

all sockets 20A or less to be an RCD, unless you had a single socket with 'freezer only' written on it

The ordrinary/skilled persons bit is awkward - lets be hones you are NOT gonna get away with that in a house.

Anyway, its irrelevant because all cables less than 5 cm from the surface have to be RCD protected if insalled in the safe zones and not in earthed metallic conduit.
 
feel stupid now, you now what its like tho, you sieve through the big brown/red book for so long looking up things that eventually your mind blanks out over simple things.
 
nah its alright, at least you, me, others can get a better understanding of certain areas. I think the more you discuss stuff the better, rather than having the little voice in your head repeat the regulation all the time trying to get what it means.
 
What do you have to do with your 16th edition testers??
I need to purchase one and the little man in the shop said that he had no 16th edition ones in stock and he was waiting for the 17thedition ones to come in.
Does that mean that if you already have a 16th edition tester you ahve to get a new one??
If so what changes on them??
 
Just going back to the remark that Tony (My new Hero - are you Tony Cable ? the face of the NIC ?) made re the freezer socket having to be on an RCD. It wouldn't if it was wired surface. Does this mean the return of the surface rewire? well on the lighting and fixed equipment anyway. Are we not dumbing down by insisting everthing is on an RCD to accommodate the DIYer and worse than that the Kitchen Fitter?
Finally an unrelated RANT
i returned to a house i rewired in 2004 the other day to swap a spur to a socket outlet (which had been the boiler supply (own circuit fixed equipment & on non rcd side of split load) when i wired it. I enquired to the home owner why the Gas Board had not wanted to re-route the circuit, which would have been dead easy and where the new boiler in rthe new position was now fed from. My worst fears were confounded. They had spurred of off the Immersion Heater!! but hey they part P'd it so that's ok. Sludgy Rats
Rant Over
 
What do you have to do with your 16th edition testers??
I need to purchase one and the little man in the shop said that he had no 16th edition ones in stock and he was waiting for the 17thedition ones to come in.
Does that mean that if you already have a 16th edition tester you ahve to get a new one??
If so what changes on them??

Evo,

Only changes to testing that i am aware of for the 17th are the IR values, test voltage will be the same, but values all move 'up one' (@500V min now 1Mohm instead of 0.5Mohm)

Heard rumours that ramp testing of rcd's was gonna come in (so you record actual trip current instead of/as well as trip time, but it doesnt look like.

Seen lots of '17th editon testers' out there. Perhaps they come with a little pull out 5cm ruler so you can check the depth of cables below the surface!!!!!

And no, Andy, I am NOT Tony Cable. But by a happy coincidence my last name is 'Overcurrent Protective Device', comes from my fathers side i think.:)

Are you Andy Impedence by any chance, perhaps Andy Adiabatic Formula?
 
luke,

I am saying that iam not aware of any changes that could justify calling something a 17th edition tester

Could you imagine them introducing something that made thousands of 500-700 quid meters redundant???!!!!

Oh, and i've got some 17th edition compliant pens for sale, and ,erm...... some old socks

10 quid each

They are more expensive than the 16th edition ones, because they are, well,......17th edition!!;)
 
Tony your a man that might know.
I've been in the wholesalers this morning & while chatting to the usual crowd we got on to the 17th ed test meters. I said (same as you) as far as I was aware only the IR values had changed so all 16th ed meters will comply unless they are pass/fail type set for 16th ed results.
But one of the lads said he was told by IET (he rang them for advise on 2382 courses) that the current continuity test current( Test current I = 200 mA)
is to be changed in the first set of ammendments mid to late Feb (I've found nothing on the IET site about it).
He also said to hangfire with the 2382 courses due to said ammendments.
Just wondered if you or anybody else had heard anything or is it the usual rumour mill on the go.
 
Last edited by a moderator:
Test equipment need not be changed, there is no difference between 16th & 17th edition testers. This is the nos. you need to look at IEC 61010 & EN 61557 if your meters comply to these your ok. Hope this helps.
 
Has Anyone Spotted Any Mistakes In The Big Red Bible Yet,page 363 Radial Final Circuit Arrangements Reg 433.1 "a Radial Final Circuit Starts And Finishes At The Distribution Board And Is Protected By A 30a Or 32a Protective Device,"hmmmmmm.sounds More Like A Ring To Me.ha.anybody Would Think The New Regs Where Rushed In.
 

Reply to Changes in the 17th edition.... in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
272
After a bit of advice as it seems starting from scratch and becoming a member of NIC or similar has mixed reviews on here.... Looking at starting...
Replies
4
Views
1K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi, First time posting on here so apologies if I'm missing any basic information, but hopefully someone can help me as an amateur DIY-er and...
Replies
10
Views
5K
A bit of a mini essay but these questions have been building up in my mind over the last weeks and months as I've been studying and volunteering...
Replies
6
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock