Discuss Changing original 32Amp contactors for solid state relays? in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

Yonny24

DIY
Reaction score
34
Hi Guys,

My underfloor heating has 3 x 32amp contactors. They make a hell of a thump when opening and closing. Bit of a hum also.

I'm looking at the idea of changing them for solid state relays like this one Solid State Relay - 40A (3-32V DC Input) - COM-13015 - SparkFun Electronics - https://www.sparkfun.com/products/13015

Will these work? I'd need to source a 12v switching supply instead of the current 220v. Easily done as I have plenty of 220-12v power supplies handy.
I assume they are much quieter and can be switched endless times without any physical parts wearing out.

Thanks in advance
 
In theory, yes. You can also get types with 230V AC control input. Depending on the current they are switching, a heatsink may be required as unlike a contactor, there is a small voltage drop across the power device that results in some heat dissipation (although, there's no heat dissipation from the control side as there is in a contactor coil.) Read the data sheet. Depending on the supply voltage, likelihood of voltage spikes and the nature of the load (yours is resistive and therefore should be tame) snubbers and/or transient voltage suppression might be recommended.

My experience with power semiconductor devices is that you get what you pay for. I don't know about the particular product in your link but an industrial SSR of that rating, that I would be happy to rely on, is typically more expensive.
 
You might want to investigate 'silent contactors' to replace your present ones. Here is an example:

View: https://www.amazon.co.uk/Hager-Esc440s-Silent-Contactor-40a-4no-230/dp/B0062X1D2I


These use the usual mains supply voltage to power their coils. Other manufacturers make them too.
Thanks .

That's the one I have for the upstairs floor heating.
Yes it is silent. 40 amp model for all the heating upstairs.

Downstairs we have 3 contactors of 32 amps each but I don't think they consume more than 5000 watts in total. (230v).


5000 watts would be 22 amps in total. hmmm why have 3 x 32 amps? (maybe just what they had and the max amperage is not that important)
Wouldn't one or 2 of these be sufficient in the placement of the 3 noisy contactors?

Also the power prior to the contactors come from 3 x 20amp trip switches.

Thanks for the replies today
[automerge]1587488546[/automerge]
I see the types of heat sinks available now.

View: https://www.amazon.co.uk/SSR-40-3-32V-24-380V-Solid-State/dp/B07JQ2S3Z9/ref=pd_sbs_328_6/259-1440324-8968235?_encoding=UTF8&pd_rd_i=B07JQ2S3Z9&pd_rd_r=2d4cd923-0e7c-478f-b7a4-b92b29eeb364&pd_rd_w=87mxm&pd_rd_wg=XGJ4t&pf_rd_p=2773aa8e-42c5-4dbe-bda8-5cdf226aa078&pf_rd_r=X4E4Y1A3XRD1EP9X00WG&psc=1&refRID=X4E4Y1A3XRD1EP9X00WG


I wonder is 16 amps through a 40amp version will keep cool without a heatsink?
 
Last edited:
A wiring drawing and some pictures would be helpful plus exact numbers for the Ipower of under floor heating pads, cables, tiles. Please include the thermostats. This will help folk advise you.
 
Here we have the ground floor contactors. 4 thermostats (cheap copies of Honeywell and do not work well at all). Installing a central digital thermostat that will send a signal to the sonoff switch in the fuse box.

Living room
Dining room
Breakfast room and kitchen (2 zones).

Living room about 11-12m2 consumes about 2000 kwh.
Dining room a little less and kitchen/breakfast about 1800 combined.

No more than 6000 kwh. (230v)

Would it be possible to swap out the 3 contactors here for 1 x 4 pole new contactor? How would this be wired? You see we have 2 Lives/ 1 Neutral cable set up coming in.
I see 3 sets of L/N cables going out to each of the 3 zones. I recently added the meters.
 

Attachments

  • therm.jpg
    48 KB · Views: 27
  • thumbnai1.jpg
    102.8 KB · Views: 29
  • thumbnail.jpg
    137.1 KB · Views: 31
  • thumbnail2.jpg
    121.2 KB · Views: 30
  • thumbnail5.jpg
    102.3 KB · Views: 29
Could you take a couple more photos? One looking down on the black bar across the top of the 20A circuit breakers and one looking up to the contactors, timer and power meters?

It looks to me that the power meter and the time switch are unused - am I correct?

The wiring looks somewhat quirky so the extra photos will be helpful.

Who wired this up?
 
Many thanks Marconi. Appreciate your time.

The timer on the right is now unused. Just the L/N being taken from the inputs to power the Sonoff R3 wifi switch on the left that I added this week to control the contactors. Much easier to set times and control virtually.

The 3 slim power meters I added are in use as I'm currently calculating the costs and making notes of daily use. They are wired in between the 20amp breakers and the contactors. (They are upside down as the inputs were on the bottom oddly). Sorry the double cabling (2 x 2mm) was used on the meters as I did not happen to have any 3mm in the house. I'll get around the changing those and making it all neater once the lockdown is over.

The original wiring with the breakers and contactors was all done by the underfloor heating company 'EuroCable' 10 years ago when the house was constructed.

Struggled at first to figure out the L1/L2/N 3 wire cabling config.

Thanks again
 

Attachments

  • thumbnail6.jpg
    96.6 KB · Views: 24
  • thumbnail7.jpg
    78.3 KB · Views: 24
Last edited:
Sir- could you tell me please what qualifications and experience you have with this type of wiring and electrical accessories?

What I am seeing looks 'confused'. For example the power meters look to be wired across the 20A circuit breakers. The wiring arrangement of the top row of disconnector and 5 circuit breakers is as I said before quirky. And I cannot fathom why you reckon you have an L1, L2 and N power supply. There are other anomalies.
 
Sir- could you tell me please what qualifications and experience you have with this type of wiring and electrical accessories?

What I am seeing looks 'confused'. For example the power meters look to be wired across the 20A circuit breakers. The wiring arrangement of the top row of disconnector and 5 circuit breakers is as I said before quirky. And I cannot fathom why you reckon you have an L1, L2 and N power supply. There are other anomalies.


No qualifications but many years experience of building valve amps/rebuilding transistor amps, home electrics also over the last 20 odd years.

The output of each 20a circuit breaker is wired to the meter and the output of the meter goes into the contactor.

The original cables (The thick white and brown cables) that were between the 20a breakers and contactors were just swapped over to the power meters inputs - nothing changed there.

230v, 209v, 23v - readings from ground to main cabling entering the main breaker.

Thanks
 
What is that black bar along the top of the 5 cbs? It looks like it connects together the top five terminals and is supplied by 3 white wires from under the disconnector connected to its terminals N, L1 and L2.

And a thin Blue (neutral) connects to the underneath terminal of the second from right cb which seems odd to me.

Could you point out to me the main neutral entering and being distributed please?

Are those five cbs double pole types?

Where did you measure those voltages you mentioned in #10?
 
ok adding some original photos here of the previous original wiring.
[automerge]1587564362[/automerge]
What is that black bar along the top of the 5 cbs? It looks like it connects together the top five terminals and is supplied by 3 white wires from under the disconnector connected to its terminals N, L1 and L2.

And a thin Blue (neutral) connects to the underneath terminal of the second from right cb which seems odd to me.

Could you point out to me the main neutral entering and being distributed please?

Where did you measure those voltages you mentioned in #10?

What is that black bar along the top of the 5 cbs? - Not sure that was original - appears to apply the power across all 5 cbs from all 3 cables as if they are all live. Yes from the 3 white wires from the main breaker.
I have the same upstairs.

That small blue wire suppliers the Live/positive to the timer.
The 3rd white cable coming into the main breaker is the one with 23v to ground. I haven't gotten my head around the 3 cable config yet. You can see they've used the small white wire from the final 20a breaker to supply the neutral for the timer.

I measure those voltages from the ground bus to the 3 main contacts on the 1st main breaker top left.

Original timer on the right was connected from the bottom outlets to each contactor. I removed the outputs as I have the sonoff now on the left.

Hope this helps. If you need more photos/details please ask.
Maybe Uruguayan standards?? I'm an expat from the UK so was odd for me.

Thanks again
 

Attachments

  • thumbnail5.jpg
    102.3 KB · Views: 19
  • thumbnail9.jpg
    102 KB · Views: 22
Last edited:
Thank you. I am being careful to understand how it is wired now. Eventually I will produce a drawing.
[automerge]1587566140[/automerge]
Could you , with great care, study your main consumer unit and establish where the group of three whites above the did connector are supplied from and post a picture. Don,t go sticking your fingers it tools inside to do this. Can you also identify the neutral for the under floor heating and what it connects to. Last take a picture of your main electricity meter(s).
 
Last edited:
ok let me try this.

The 3 white cables are wired from an identical adjacent fuse box. These are fed from an identical main breaker (did?). All in the same sequence. Other breakers to supply lights/sockets etc come from the first fuse box.

The main cable coming into the house has these 3 cables feeding into the did/breaker.
Outside we have a breaker at the front gate. The 3 red wires shown are the ones that come into the 1st main fuse box - same sequence again and then into the second box for the floor heating.

Not sure about the neutral.

I can see from the thermostats the cables from the contactors are fed onto the 1st and 2nd screws (must be live and neutral, left live, right neutral). Behind the thermostat you see the orange cables that must be leading to the floor. These do not have a floor thermostat, just air. Looks like the main white connects to the orange and the other orange to the blue. Live and neutral.

4 thermostats here. 2 from one contactor 'kitchen' must be in series, 1 for the living room, and one for the dining room.
[automerge]1587568267[/automerge]
Been studying the house for some months now. We moved in last year.
been installing cat6 through the conduits, changing all the wall sockets, adding intelligent lights switches and routers etc.

Found a lot of odd things. Don't even ask me about the main grounding of the house and pool area! All fixed now luckily.
 

Attachments

  • thumbnail10.jpg
    184.6 KB · Views: 21
  • thumbnail11jpg.jpg
    59.7 KB · Views: 20
  • thumbnail12.jpg
    68 KB · Views: 20
Last edited:
Other side of the wall. Thick Grey cable is the supply from the overhead street cables.
 

Attachments

  • IMG_20200422_122027.jpg
    82.7 KB · Views: 16
  • IMG_20200422_122000.jpg
    96.1 KB · Views: 15
  • IMG_20200422_122012.jpg
    83.6 KB · Views: 17
It must be getting late where you are. So one last photo please looking up underneath the meters to see the individual wires going into it. Then I will leave you be until tomorrow. I am going to cook some minty lamb mince Devon pasties.


Not 'did' - meant to type disconnector or main breaker if you prefer.

Where are you in Uruguay? I am in London.
 
Sounds tasty. Miss many things from the UK.
We're 4 hours behind the UK so on my lunch break now. Work remotely here.
I live in Barra de Carrasco, Canelones. Just outside Montevideo.
Tricky to take photos as the meter is in a big sealed box with a small window just big enough to get my hand in.

Bon Appétit or buen provecho.
Regards
 

Attachments

  • IMG_20200422_124811.jpg
    60.9 KB · Views: 18
  • IMG_20200422_124813.jpg
    103.2 KB · Views: 26
Good morning. I will start to produce some drawings today. First though please tell me the colours of the wires in the thick supply cable under the meter.

From the meter box it looks like 3 reds head out to your home and no other wires - is this correct? What colours do they connect to at the meter? If you cannot say then please make a drawing for me.

There is also a terminal schematic on the plastic cover over the meter terminals which I cannot see completely - could you draw or photo it and mark up where the wires of the supply and the 3 reds connect to?
 
Observations 1

a. If one studies Drawing 1 attached, one can observe that through the 4 pole disconnector (top left) and then the 3 white wires to above the 5 circuit breakers all the 3 white wires top left are joined together by the black busbar. This means these three white wires top left cannot be L1, L2 and N because a short circuit would have occurred rupturing a fuse or tripping a circuit breaker external to this enclosure. If a short circuit has not happened then they more likely to be of the same potential ie: a line or a neutral. The N, L1, L2 and L3 markings on the disconnector are to inform how it should be connected to such a supply if presented to it.

b. Studying further, one can readily see that each of the 2 wire digital power meters are connected across a 20A circuit breaker - this is incorrect. When the circuit breaker is closed the input to the power meter is short circuited and will not read any power consumption. In addition, the power meter requires an L and N at its input where only an L or N (yet to be confirmed) has actually been connected. I note the meters are reading zero.

c. The output side of the power meter connects to the input of a contactor by the blue and white wires and then from the output of each contactor to the floor heating elements ( I assume at this stage). Because only an L or an N (yet to be confirmed) is provided at the input to each contactor then no supply voltage will ever be connected across the elements - therefore they will not heat up. I suspect then that the underfloor heating system does not work at all at the moment.

d. The timer, albeit now redundant, still has two wires to it presumably intended as its supply - blue and white. Since these are derived wrongly from the two circuit breakers on the far right whose inputs are connected together by the black busbar there will be no voltage supply applied to the timer - it will not function.

e. From d), since the wifi switch has been tapped off the input to the timer it too has not voltage supply and will not function.

f. it would be impossible to measure with respect to earth the three voltages 230, 209 and 23V at the input terminals to the disconnector while it was closed because as mentioned when the disconnector is closed all the two sets of 3 white wires are at the same potential because of the black busbar.

It looks to me then that the wiring for the UFH was wrong from the very start or changes have been made which have resulted in a completely incorrect arrangement. Do you know the history of the UFH - did it ever work?
 

Attachments

  • drawing1.png
    47.9 KB · Views: 19
Observations 1

a. If one studies Drawing 1 attached, one can observe that through the 4 pole disconnector (top left) and then the 3 white wires to above the 5 circuit breakers all the 3 white wires top left are joined together by the black busbar. This means these three white wires top left cannot be L1, L2 and N because a short circuit would have occurred rupturing a fuse or tripping a circuit breaker external to this enclosure. If a short circuit has not happened then they more likely to be of the same potential ie: a line or a neutral. The N, L1, L2 and L3 markings on the disconnector are to inform how it should be connected to such a supply if presented to it.

b. Studying further, one can readily see that each of the 2 wire digital power meters are connected across a 20A circuit breaker - this is incorrect. When the circuit breaker is closed the input to the power meter is short circuited and will not read any power consumption. In addition, the power meter requires an L and N at its input where only an L or N (yet to be confirmed) has actually been connected. I note the meters are reading zero.

c. The output side of the power meter connects to the input of a contactor by the blue and white wires and then from the output of each contactor to the floor heating elements ( I assume at this stage). Because only an L or an N (yet to be confirmed) is provided at the input to each contactor then no supply voltage will ever be connected across the elements - therefore they will not heat up. I suspect then that the underfloor heating system does not work at all at the moment.

d. The timer, albeit now redundant, still has two wires to it presumably intended as its supply - blue and white. Since these are derived wrongly from the two circuit breakers on the far right whose inputs are connected together by the black busbar there will be no voltage supply applied to the timer - it will not function.

e. From d), since the wifi switch has been tapped off the input to the timer it too has not voltage supply and will not function.

f. it would be impossible to measure with respect to earth the three voltages 230, 209 and 23V at the input terminals to the disconnector while it was closed because as mentioned when the disconnector is closed all the two sets of 3 white wires are at the same potential because of the black busbar.

It looks to me then that the wiring for the UFH was wrong from the very start or changes have been made which have resulted in a completely incorrect arrangement. Do you know the history of the UFH - did it ever work?

Wow thanks for your detailed reply.
I'll reply to a few of the points and look into it in more detail later and get back to you.

b - The meters are working perfectly. They measure 230v across the input terminals and 230v across the outputs. They turn over and the green light flashes red when current is flowing through. The dining room was turned on last night and used 2000 kwh. Now reading 5.1 kw

c- the outputs of the meters read 230v (across the white and blue terminals) and feed the contactors. These heat up when the timer activates them. All the floor heating works.

d- the original timer on the right also has 230v across the blue and white wires. This has always worked and did switch on the contactors before I switched the timer over to the sonoff.

f- I measured the 3 voltages with respect to earth at the input of the main breaker (3 white wires).

Every contactor's input terminals has 230v across the white and blue wires and also across the output terminals when switched on (and they get hot).

Sorry to throw a spanner in the works.
I'll have a look at the external meter box later and get back to you.

Many thanks
 
That means then that what I see in the photos is inaccurate. Could you draw the wiring for me to study?

Could you confirm (safely) what the black bar along the 5 cbs is and does? Does it connect together all the top terminals?

Does the group of three whites under the disconnector go to above the 3 left side cbs.
 
That means then that what I see in the photos is inaccurate. Could you draw the wiring for me to study?

Could you confirm (safely) what the black bar along the 5 cbs is and does? Does it connect together all the top terminals?

Does the group of three whites under the disconnector go to above the 3 left side cbs.


Your drawing is fine - just the brown and white wires entering the power meters are the other way around. White entering the left terminal and brown entering the right terminal. Everything else matches up.

The black bar along the cbs just appears to join all the cables across which I find odd.
All 3 live power cables?? This will all installed by the authorised national electricity company here, UTE, to their standards.


Yes the group of white wires under the disconnector go above to the 3 cbs in the same sequence also. Left to right.
 

Attachments

  • powerbus.jpg
    74.8 KB · Views: 17
Only if you feel safe to do so - would you measure and report the voltages at each of the top three terminals ( 1, 3, 5) of the disconnector to earth and then do the same for the corresponding bottom 3 terminals ( 2 , 4 ,6 )? Ac voltage and a scale to read at least 230V.
 
Only if you feel safe to do so - would you measure and report the voltages at each of the top three terminals ( 1, 3, 5) of the disconnector to earth and then do the same for the corresponding bottom 3 terminals ( 2 , 4 ,6 )? Ac voltage and a scale to read at least 230V.
Will do.
Yes I feel safe to do this. I've worked with valve amps, 500v transformers for power outputs and high amperage power supplies for valve heaters etc, and 400+v caps for years. These caps pack a punch even when disconnected. I know what it's like to get a shock and not pleasant (or safe). A charged disconnected cap can cause a lot of pain.
[automerge]1587645878[/automerge]
Only if you feel safe to do so - would you measure and report the voltages at each of the top three terminals ( 1, 3, 5) of the disconnector to earth and then do the same for the corresponding bottom 3 terminals ( 2 , 4 ,6 )? Ac voltage and a scale to read at least 230V.


1 (top 1st terminal) - 258
3 (top 2nd terminal) - 28
5 (top 3rd terminal) - 240

2 (bottom 1st terminal) - 214
4 (bottom 2nd terminal) - 26
6 (bottom 3rd terminal) - 238

All measured to ground.
 
Last edited:
Thank you.
If 2, 4 and 6 out of the disconnector were indeed linked together by the black bar above the cbs then the voltage would be the same on each - which is not the case.

So to check further please measure between each of the top terminals of the 5 cbs to earth and then do the same for the bottom terminals to earth.
 
Thank you.
If 2, 4 and 6 out of the disconnector were indeed linked together by the black bar above the cbs then the voltage would be the same on each - which is not the case.

So to check further please measure between each of the top terminals of the 5 cbs to earth and then do the same for the bottom terminals to earth.

This may shed some light on the set up and function of the bus now.

Top CBS
1-202
2-24
3-224
4-202
5-24

Bottom CBS
1-202
2-24
3-224
4-202
5-24
 
Yes that I think has resolved much.

At you convenience could you measure at the disconnector the voltage between:

a. 1 and 2, then between 3 and 4 and lastly 5 and 6 ie: across the poles of the disconnector. Why? Because you measured 258V at 1 and 214V at 3 which indicates to me a problem with this pair of contacts - so we will check them all.

b. 1 and 3 to establish you have a 3 phase supply ( 1 to 3 will be 230V ish) or a split phase supply ( 1 to 3 will be 460V ish) - I am pretty sure it is a three phase supply with one line earthed to produce L1, L2 and N (L3 earthed) all phased 120 degrees apart.

The evidence from the voltage readings suggests to me how the panel is wired which I will now draw out.
 
ah wait think my scribbles of the voltage of 1 was wrong - let me just check.

my apologies - running up and down in between work tasks
[automerge]1587652801[/automerge]
ok that is odd. Not sure why I measured them so differently before. Washing machine is on now. This should have no relevance unless there is an issue somewhere. I'll test again later

Here goes again sorry: (this makes more sense)

1 (top 1st terminal) - 208
3 (top 2nd terminal) - 24
5 (top 3rd terminal) - 230

2 (bottom 1st terminal) - 208
4 (bottom 2nd terminal) - 24
6 (bottom 3rd terminal) - 230

Top CBS
1-208
2-24
3-230
4-208
5-24

Bottom CBS
1-208
2-24
3-230
4-208
5-24
 
Last edited:
The UFH heating is cleverly connected across L1, L2 and N as shown in the diagram below. The black bar above the 5 cbs confused me; the voltage measurements clarified the situation.

Sometime please tell me L1 to L2 voltage. I am pretty sure you have a 3 phase supply arranged as I have drawn.

Otherwise I would swap the contactors for silent ones. Solid state switches can fail short-circuit which would not be a good thing so don't fit them. They also need substantial heatsinks and ventilation around these because they would get too hot without. If it was me I'd buy silent contactors. The three sets of UFH are each protected by a 20A cb. A 32A contactor is beefy enough to carry up to 20A 'all day long' and be more reliable than one rated close to 20A. Space the power meters and contactors apart so that there is some air movement and one does not warm the other.

Thank you for your patience!

:)

Marconi
 

Attachments

  • diagram2.jpeg
    63.2 KB · Views: 13
The UFH heating is cleverly connected across L1, L2 and N as shown in the diagram below. The black bar above the 5 cbs confused me; the voltage measurements clarified the situation.

Sometime please tell me L1 to L2 voltage. I am pretty sure you have a 3 phase supply arranged as I have drawn.

Otherwise I would swap the contactors for silent ones. Solid state switches can fail short-circuit which would not be a good thing so don't fit them. They also need substantial heatsinks and ventilation around these because they would get too hot without. If it was me I'd buy silent contactors. The three sets of UFH are each protected by a 20A cb. A 32A contactor is beefy enough to carry up to 20A 'all day long' and be more reliable than one rated close to 20A. Space the power meters and contactors apart so that there is some air movement and one does not warm the other.

Thank you for your patience!

:)

Marconi

I'll get back to you soon - just had an incident where my wife's car battery died completely when she needed to go out most- looks like a dead cell. 3v when disconnected!!

Not a happy wife at the moment. (apparently my fault for buying a GM car)
 
My last missive for today - Lucien Nunes is the chap if you want to discuss valve amplifiers.

Corrigendum: the disconnector also includes a 40A cb in each pole which I did not make clear - before my colleagues correct me ;-)
 
Any chance of a picture of your meter(s)?

Sorry haven't got around to that yet. Home schooling after work till 10pm then bed due to early zoom meetings.

Just now I measured the voltages across the terminals of the main disconnector breaker.
225/226v across each one. 1-2, 1-3, 2-3.

So we have a 3 phase supply by the looks of it.

Now what kind of new contactor would I need for the 3 zones and how to wire this up properly?

Many thanks
 
It is not easy for me to research the brands available in Uruguay. What I suggest you do is google or go to an electrical supplier and look for:

1. Silent contactor - the ac mains applied to A1 and A2 is rectified inside the contactor and then used to energise the coil.
2. Double Pole
3. At least 32A ac resistive load rating ie: low inductance like the UFH load.
4. 220-240V ac supply for coil (but see 1 above).
5. DIN rail fitting.
6. Study the number of switching operations figure - to handle a large number of open/close contact actions at rated current is a sign of 'goodness' so a high value to be preferred to a contactor with a low/lower figure.

Once you have found some options I will check them before you purchase should you wish.

The digital power meters are wired before the contactor as now. You will though ditch the doubled up 2mm2 for a single suitable 4mm2 wire.

With regards to wiring them in to the control logic - are you using your phone/wifi and SONOS switch to replace the timeswitch? And this then provides the live feed to the zone thermostats? The switched live from the zone thermostats then provides the A1 input to the corresponding zone contactor with a Neutral being provided to the A2.

Or are you going to have wifi thermostats too some of which incorporate a time/day programmer?

Or are you going to go the whole hog and introduce smart home technology to control the UFH? If so you would be better off starting a new thread and exploring options with EF colleagues who install this for a living. Once you have contactors you can apply a switched live to them via wifi switches which you can interface with smart home technology. My neighbour has British Gas HIVE but there are other suppliers.

Regards

Marconi
 
It is not easy for me to research the brands available in Uruguay. What I suggest you do is google or go to an electrical supplier and look for:

1. Silent contactor - the ac mains applied to A1 and A2 is rectified inside the contactor and then used to energise the coil.
2. Double Pole
3. At least 32A ac resistive load rating ie: low inductance like the UFH load.
4. 220-240V ac supply for coil (but see 1 above).
5. DIN rail fitting.
6. Study the number of switching operations figure - to handle a large number of open/close contact actions at rated current is a sign of 'goodness' so a high value to be preferred to a contactor with a low/lower figure.

Once you have found some options I will check them before you purchase should you wish.

The digital power meters are wired before the contactor as now. You will though ditch the doubled up 2mm2 for a single suitable 4mm2 wire.

With regards to wiring them in to the control logic - are you using your phone/wifi and SONOS switch to replace the timeswitch? And this then provides the live feed to the zone thermostats? The switched live from the zone thermostats then provides the A1 input to the corresponding zone contactor with a Neutral being provided to the A2.

Or are you going to have wifi thermostats too some of which incorporate a time/day programmer?

Or are you going to go the whole hog and introduce smart home technology to control the UFH? If so you would be better off starting a new thread and exploring options with EF colleagues who install this for a living. Once you have contactors you can apply a switched live to them via wifi switches which you can interface with smart home technology. My neighbour has British Gas HIVE but there are other suppliers.

Regards

Marconi

Hi Marconi.


No not easy for any of us to research items here. Nothing like screwfix etc.

Can I use one 40A contactor to replace all 3? Using the 3 poles of a 4 pole contactor?

This year currently got one sonoff temperature probe (TH10) in the living which will have a schedule and temperature range (from the app/amazon/IFTTT) and in turn activate the other sonoff R3 inside the fusebox to energize A1/A2. I imagine 95% of the time it will be switched on for the few hours it will be on a day.

Maybe in the future if we continue using the floor heating I'll look at more advanced systems to control each zone.

Many thanks
 
Nearly on the outside of a bottle of wine now so to be safe I will answer tomorrow morning.

Until then it'd be useful to know what you want to achieve in terms of functionality for each zone now.
 
Nearly on the outside of a bottle of wine now so to be safe I will answer tomorrow morning.

Until then it'd be useful to know what you want to achieve in terms of functionality for each zone now.

almost 6pm in the UK so ok for me to crack open a bottle now? Probably not yet as I'm preparing SQL scripts for a major live deployment on Monday! (Database developer)

Salud!
[automerge]1587747269[/automerge]

[automerge]1587747615[/automerge]
We're also going to evaluate the cost of running the UFH this winter. We had plans to install another heating system (plus double glazing) but the global crisis put a stop to that.

I love the UFH but been calculating the costs and will be about 1 GBP per hour. That soon adds up. 9-10 kwh for both floors. We'll be testing a different number of zones to see how much we need on to heat the house sufficiently.
 
Last edited:
How much is a kWh day and night? We buy our gas and leccie from EDF (Electricite de France) and have Economy 7 so cheap 7 hours overnight 0000-0700 GMT at:

Electricity day unit rate: 15.67p per kWh
Electricity night unit rate: 9.73p per kWh
Daily standing charge: 23.86p per day

Gas unit rate: 2.870p per kWh
Daily standing charge: 20.48p per day
 
How much is a kWh day and night? We buy our gas and leccie from EDF (Electricite de France) and have Economy 7 so cheap 7 hours overnight 0000-0700 GMT at:

Electricity day unit rate: 15.67p per kWh
Electricity night unit rate: 9.73p per kWh
Daily standing charge: 23.86p per day

Gas unit rate: 2.870p per kWh
Daily standing charge: 20.48p per day

We have the double tariff plan. (single, double and triple available) If you have triple 00:00-07:00 is even cheaper but then 7am-5pm is a bit more expensive. We have a pool with pump/filter running 7-8 hours until 5pm so the triple tariff is not worth it for us.

Also just had a 10% increase in prices this year. Normal developing world inflation!!


11pm - 5pm: 4.6 pesos kWh (8.64 pence)
5pm - 11pm: 11.59 pesos kWh (21.77 pence)
monthly fixed charges: £35 more or less


Our fixed charges are quite high as we have 15kW available. You can have a smaller kW available with less fixed charges but obviously that won't work with UFH. Also we have A/C for the summer. Years ago in a small flat we had A/C and kept tripping the main breaker due to the small kW available.

Dinner time gets expensive with the oven and hob at 22 pence per kWh! Unless you are very organized and cook before 5pm!

I was with ovo in Lichfield, UK. Was impressed with them and worked out fairly cheap on the dual tariff.
[automerge]1587752411[/automerge]

[automerge]1587752566[/automerge]
Btw this is the contactor used for the 1st floor. 3 bedrooms, landing and 2 bathrooms. All through this one 4 pole. Split into 2 zones (2 cbs). Super silent 40a.
 

Attachments

  • 1stfloor.jpg
    60.8 KB · Views: 6
  • 1stfloor.jpg
    60.8 KB · Views: 7
Last edited:
I was thinking. Upstairs the small zones don't pull much current.
There is a contactor for 4 zones.
The small landing for example only pulls about 800-1000w?
Surely I can safely wire this directly from the 16amp CBS to a wifi switch of 10-16amps instead of the contactor?
 
ABB ESB40-40-230AC/DC - https://new.abb.com/products/GHE3491102R0006/esb40-40-230ac-dc-installation-contactor

The ABB contactor is a good make and well suited. It is a silent or hum-free design and the 40A AC1 (resistive and low inductance or PF nearly 1) rating for the contacts is excellent for your application.

I don't know what the Uruguay electrical regulations stipulate for switching to countenance single pole switching. At the moment all your contactors are used for double pole switching; this is certainly necessary for those UFH elements wired across L1 and L2 but for those across L1-N and L2-N single pole may be allowed - I just don't know. However, double pole is to be preferred because it maintains uniformity of wiring scheme for the UFH system and there is some advantage in splitting the arc across two pairs of contacts when they open to prolong life. I would not opt for single pole switching.

The aforesaid means that to continue with double pole switching you would need to obtain a 6 pole contactor if you wanted one to switch three sets of heating elements in the way a showed in my last diagram. Such a contactor I is rarer than 4 pole and thus I expect pricier. I don't know if you can obtain a silent 6 pole contactor.

Using one contactor to switch 2 or more UFH zones has two drawbacks; if it fails you have lost all heating and when it closes or opens the large current change will cause a noticeable and perhaps troublesome voltage transient in your home and maybe to your neighbours. Far better to sub-divide the load switching over 3 contactors to reduce the magnitude of each transient step. Already I notice that you have quite a variation in supply voltage as loads in your home are powered on and off which indicates a higher supply impedance than is typical in the UK. Switching the UFH zones as one will be noticeable and annoying.

Which leads on to the idea of switching each zone directly using a wifi 'contactor'. In theory this is possible but great care is needed to ensure the power contacts have an adequate AC1 rating and can cope with frequent switching during the day. I'd have to see the specification to comment further. Would it be silent? Would I do it in 'one step'? - no, because I like my functionality appropriately realised in the best possible way. I speak from an industrial background so in the domestic setting one might be more inclined to economy of components.

Sorry about the rather long-winded reply - I have nothing else to do.

:)
 
ABB ESB40-40-230AC/DC - https://new.abb.com/products/GHE3491102R0006/esb40-40-230ac-dc-installation-contactor

The ABB contactor is a good make and well suited. It is a silent or hum-free design and the 40A AC1 (resistive and low inductance or PF nearly 1) rating for the contacts is excellent for your application.

I don't know what the Uruguay electrical regulations stipulate for switching to countenance single pole switching. At the moment all your contactors are used for double pole switching; this is certainly necessary for those UFH elements wired across L1 and L2 but for those across L1-N and L2-N single pole may be allowed - I just don't know. However, double pole is to be preferred because it maintains uniformity of wiring scheme for the UFH system and there is some advantage in splitting the arc across two pairs of contacts when they open to prolong life. I would not opt for single pole switching.

The aforesaid means that to continue with double pole switching you would need to obtain a 6 pole contactor if you wanted one to switch three sets of heating elements in the way a showed in my last diagram. Such a contactor I is rarer than 4 pole and thus I expect pricier. I don't know if you can obtain a silent 6 pole contactor.

Using one contactor to switch 2 or more UFH zones has two drawbacks; if it fails you have lost all heating and when it closes or opens the large current change will cause a noticeable and perhaps troublesome voltage transient in your home and maybe to your neighbours. Far better to sub-divide the load switching over 3 contactors to reduce the magnitude of each transient step. Already I notice that you have quite a variation in supply voltage as loads in your home are powered on and off which indicates a higher supply impedance than is typical in the UK. Switching the UFH zones as one will be noticeable and annoying.

Which leads on to the idea of switching each zone directly using a wifi 'contactor'. In theory this is possible but great care is needed to ensure the power contacts have an adequate AC1 rating and can cope with frequent switching during the day. I'd have to see the specification to comment further. Would it be silent? Would I do it in 'one step'? - no, because I like my functionality appropriately realised in the best possible way. I speak from an industrial background so in the domestic setting one might be more inclined to economy of components.

Sorry about the rather long-winded reply - I have nothing else to do.

:)
Many thanks for the full write up.
I'll look for 3 abb contactors following your advice.
Now the upstairs box is a right mess and I want to tidy it up.
Looks like we have 1 contactor for 4 zones. 4 live cables going out but one neutral for each 2 live cables. Live cables on terminals 2 and 3(2 coming out of each). I'll need to draw this out as looking at the mess it's impossible to see. I traced which wires go to which ufh last night as I want to control my office ufh independently.
 

Attachments

  • IMG_20200420_202803.jpg
    109.1 KB · Views: 7
As you are the father, spouse and breadwinner please take heed of this: If you are going to be putting your fingers in among the wiring you must invest in an approved voltage indicator in order to prove dead once you have de-energised and isolated. A digital voltmeter or a neon screwdriver are not reliable. You do not need to spend much. I have a DILOG because they are good value for money and I rarely do any work these days preferring to employ an electrician for anything major.

ISOPK2 | Di-LOG - https://www.dilog.co.uk/product/isopk2/

Time spent discovering how things have been wired is well spent - do not assume anything.
 
Last edited:
As you are the father, spouse and breadwinner please take heed of this: If you are going to be putting your fingers in among the wiring you must invest in an approved voltage indicator in order to prove dead once you have de-energised and isolated. A digital voltmeter or a neon screwdriver are not reliable. You do not need to spend much. I have a DILOG because they are good value for money and I rarely do any work these days preferring to employ an electrician for anything major.

ISOPK2 | Di-LOG - https://www.dilog.co.uk/product/isopk2/

Time spent discovering how things have been wired is well spent - do not assume anything.
Thanks for the link of suggested equipment Marconi. Sound advice.

I've done a sketch of how I believe 2 of the rooms are wired up upstairs. From one of the 4 pole outlets they have 2 live wires going to each room. Just one blue neutral though on series. I would like to have these 2 controlled rooms controlled independently. Not sure how that would be achieved without installing a new digital thermostat on the wall. Would like to have them cabled independently like I do downstairs with the double pole contactors or something similar. They only draw about 1000w each.
 

Attachments

  • IMG_20200425_174048.jpg
    50.7 KB · Views: 5
Good morning. Re #44. Could you measure the voltage between earth and the red and then the blue on the supply side of the contactor to establish their potential please. I suspect they are connected to L1 and L2.
 
Did you spot the danger in the wiring shown in your picture in #42? You will have to sleeve the red conductor or shorten it. Until then keep your fingers out!

The zone you mention is fed across L-N and I am pretty sure L2-N because your L2 is higher voltage than your L1 in previous readings.

You will need two double pole contactors each supplied by the same L-N pair as now.

Each of the elements is then fed by a double pole output from one or the other contactor.

Alas, you will have to run in a new neutral to the point where the elements' Ns are joined - but you expected the requirement to do that. It was lazy wiring not to run one in the first place. Use the same thickness cable as now.

You can then think about one of these wireless thermostats and receivers for each element such as these:

Honeywell RF DT92E1000 Wireless Digital Room Thermostat | ElectricalDirect - https://www.electricaldirect.co.uk/product/honeywell-rf-dt92e1000-wireless-digital-room-thermostat-611235?vat=1&shopping=true&gclid=Cj0KCQjwhZr1BRCLARIsALjRVQP_fehCHwVa2GQkvKOaTv03u74WSe2iyqTlWLn4Ehsbqn3kHMTNCMcaAqTsEALw_wcB

Or a programmable wireless thermostat like this one:

2 in 1 Programmable Wireless Room Thermostat - 22874 - Controls | BES.co.uk - https://www.bes.co.uk/2-in-1-programmable-wireless-room-thermostat-22874
 
Did you spot the danger in the wiring shown in your picture in #42? You will have to sleeve the red conductor or shorten it. Until then keep your fingers out!

The zone you mention is fed across L-N and I am pretty sure L2-N because your L2 is higher voltage than your L1 in previous readings.

You will need two double pole contactors each supplied by the same L-N pair as now.

Each of the elements is then fed by a double pole output from one or the other contactor.

Alas, you will have to run in a new neutral to the point where the elements' Ns are joined - but you expected the requirement to do that. It was lazy wiring not to run one in the first place. Use the same thickness cable as now.

You can then think about one of these wireless thermostats and receivers for each element such as these:

Honeywell RF DT92E1000 Wireless Digital Room Thermostat | ElectricalDirect - https://www.electricaldirect.co.uk/product/honeywell-rf-dt92e1000-wireless-digital-room-thermostat-611235?vat=1&shopping=true&gclid=Cj0KCQjwhZr1BRCLARIsALjRVQP_fehCHwVa2GQkvKOaTv03u74WSe2iyqTlWLn4Ehsbqn3kHMTNCMcaAqTsEALw_wcB

Or a programmable wireless thermostat like this one:

2 in 1 Programmable Wireless Room Thermostat - 22874 - Controls | BES.co.uk - https://www.bes.co.uk/2-in-1-programmable-wireless-room-thermostat-22874

Thanks Marconi. If you feel the urge a diagram would be very helpful thanks.

Yes looks like the 2 other zones have the same set up. (using the 1st and 2nd poles each going to 2 zones). 6 zones in total from the 3 poles.

btw that black tape on the red cable is just holding the 3 wires in a bundle don't worry no connections under the insulating tape. Looks like they ran out of cable ties!! A lot of laziness in this set up.
 

Reply to Changing original 32Amp contactors for solid state relays? in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

Similar Threads

Hi All; I have a flat with 6 areas warmed via underfloor heating. Each of the areas are controlled by its own thermostat Microline Ultra-Thin...
Replies
11
Views
5K
J
Hello all I have been sent here from Tilersforum so hopefully posting in the right place! I bought some Heatmiser 12v Network Thermostats and...
Replies
7
Views
3K
ik_cw
I

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock